#77253 - 05/16/01 06:05 PM Conduit run in front of panelboard
frodo Offline
Member
Registered: 05/16/01
Posts: 129
Loc: louisville, ky usa
can you install a 2" conduit in front of and to the left looking at the front of the panelboard (600VAC)?

as i read section 110-26 (2), (3) it appears that it would be a violation if the right edge of the conduit is lined up directly with the left side of the panelboard cover looking at it from the front. i have photos available as well.

the conduit is around 6" in front and to the left side of the panelboard....
Top
2017 / 2014 NEC & Related Books and Study Guides
#77254 - 05/16/01 07:15 PM Re: Conduit run in front of panelboard
golf junkie Offline
Member
Registered: 04/22/01
Posts: 507
Loc: York, NE
Frodo,
If you project a line out from the left side of the panelboard the area must be clear for 36" minimum straight out from the front of the panel. If the line hits the 2" conduit then it's a no-no.....if the conduit is to the left of the projected line you're OK.

Hope that makes sense, if not ask again.

GJ
Top
#77255 - 05/16/01 07:42 PM Re: Conduit run in front of panelboard
frodo Offline
Member
Registered: 05/16/01
Posts: 129
Loc: louisville, ky usa
Quote:
Originally posted by golf junkie:
Frodo,
If you project a line out from the left side of the panelboard the area must be clear for 36" minimum straight out from the front of the panel. If the line hits the 2" conduit then it's a no-no.....if the conduit is to the left of the projected line you're OK.

Hope that makes sense, if not ask again.

GJ


thanks,
i have a contractor that i am supervising and they have installed a 2" conduit so close to the rule it is questionable in my mind. as i read in 110-26 (3) i must consider (e) as well, in addition to the 6" maximum beyond the front of the equipment...

thank you for taking the time to reply...

regards

frodo
Top
#77256 - 05/17/01 02:57 AM Re: Conduit run in front of panelboard
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
frodo;
i'm farily sure 110-26 (3) was made for troughs, but is ok for any pipework associated with the panel.

make sure your panel door can open 90 deg.----110-26-(2) with that pipe...

Top

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 55 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals