The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Live Chat Feature
by Admin
Yesterday at 09:52 PM
Safety at heights?
by gfretwell
Yesterday at 07:16 PM
failed home inspection.
by gfretwell
Yesterday at 07:03 PM
Webmaster > Admin
by Admin
Yesterday at 05:49 PM
Old Bath Fan
by gfretwell
Yesterday at 01:38 AM
New in the Gallery:
Desk-mounted "power-board"
Top Posters (30 Days)
Admin 33
HotLine1 21
Ruben Rocha 16
gfretwell 15
Trumpy 13
Who's Online
0 registered (), 0 Guests and 174 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#77253 - 05/16/01 06:05 PM Conduit run in front of panelboard
frodo Offline
Member

Registered: 05/16/01
Posts: 129
Loc: louisville, ky usa
can you install a 2" conduit in front of and to the left looking at the front of the panelboard (600VAC)?

as i read section 110-26 (2), (3) it appears that it would be a violation if the right edge of the conduit is lined up directly with the left side of the panelboard cover looking at it from the front. i have photos available as well.

the conduit is around 6" in front and to the left side of the panelboard....

Top
2017 / 2014 NEC & Related Books and Study Guides
#77254 - 05/16/01 07:15 PM Re: Conduit run in front of panelboard
golf junkie Offline
Member

Registered: 04/22/01
Posts: 511
Loc: York, NE
Frodo,
If you project a line out from the left side of the panelboard the area must be clear for 36" minimum straight out from the front of the panel. If the line hits the 2" conduit then it's a no-no.....if the conduit is to the left of the projected line you're OK.

Hope that makes sense, if not ask again.

GJ

Top
#77255 - 05/16/01 07:42 PM Re: Conduit run in front of panelboard
frodo Offline
Member

Registered: 05/16/01
Posts: 129
Loc: louisville, ky usa
Quote:
Originally posted by golf junkie:
Frodo,
If you project a line out from the left side of the panelboard the area must be clear for 36" minimum straight out from the front of the panel. If the line hits the 2" conduit then it's a no-no.....if the conduit is to the left of the projected line you're OK.

Hope that makes sense, if not ask again.

GJ


thanks,
i have a contractor that i am supervising and they have installed a 2" conduit so close to the rule it is questionable in my mind. as i read in 110-26 (3) i must consider (e) as well, in addition to the 6" maximum beyond the front of the equipment...

thank you for taking the time to reply...

regards

frodo

Top
#77256 - 05/17/01 02:57 AM Re: Conduit run in front of panelboard
sparky Offline
Member

Registered: 10/18/00
Posts: 5545
frodo;
i'm farily sure 110-26 (3) was made for troughs, but is ok for any pipework associated with the panel.

make sure your panel door can open 90 deg.----110-26-(2) with that pipe...


Top