#7722 - 02/18/02 08:08 PM nail in anchors during fire
Elzappr Offline
Member
Registered: 12/20/01
Posts: 270
Loc: Oregon
I recall reading somewhere that "nail-in" or "hammer-set" anchors will come loose during a fire. In other words, you shouldn't use them to support electrical conduit and boxes to a concrete ceiling because they aren't rated for fire. But, everybody does. Anyone have the skoop about them?
Top
Work Gear for Electricians and the Trades
#7723 - 02/19/02 04:15 AM Re: nail in anchors during fire
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
I know that some lead anchors have restrictions on their use due to the possibility of melting during a fire. But I believe steel is OK.
Top
#7724 - 02/19/02 03:19 PM Re: nail in anchors during fire
Elzappr Offline
Member
Registered: 12/20/01
Posts: 270
Loc: Oregon
I don't think the anchors that I am referring to are made of steel..more like some sort of lead/zinc/? alloy..its pretty soft stuff.
Top
#7725 - 02/19/02 07:22 PM Re: nail in anchors during fire
spkjpr Offline
Member
Registered: 12/01/00
Posts: 218
Loc: Sedalia,MO, USA
Elzapper, I have not heard about that but it makes sense. Many moons ago when I was involved with the fire service we had major discussions about the metal plates used in truss rafters, seems in a fire they would char the wood around them and would give away with no warning. Most of the anchors are made of a lead-zinc alloy and do have a low melting point though.
Top
#7726 - 02/20/02 06:11 AM Re: nail in anchors during fire
JBD Offline
Member
Registered: 07/12/01
Posts: 599
Loc: WI, USA
For technical information on fasteners go to Powers website at http://www.powers.com/aepdf/AEnew.htm
Top
#7727 - 02/20/02 02:06 PM Re: nail in anchors during fire
Elzappr Offline
Member
Registered: 12/20/01
Posts: 270
Loc: Oregon
I've got a Powers catalog (couldn't use the link you provided because my Acrobat Reader 5.0 isn't working right..freezes my computer up!) and it says that standard Zamac Nailins AREN'T recommended for overhead use. Additionally they state that their Zamac Hammar-Screw can be used for overhead, but only if it is "designed by an engineer who will take the proper design considerations and safety factors into account." Well, nobody does that! What sort of design considerations? Fires?
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 67 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
KrmtFrg, Stack, Scotto, Freecrowder, clee512

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals