#77205 - 05/14/01 04:22 AM Wires per hole??
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
an oldie, but goodie....

how many wires can i put in a hole?

assume rx or mc thru wood joists here....


Top
2017 / 2014 NEC & Related Books and Study Guides
#77206 - 05/14/01 05:50 AM Re: Wires per hole??
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
As many as will fit in the hole. Remember that the hole must comply with 300-4 and must not destroy the structural strength of the framing member. This assumes that the cables will NOT be tightly bundled between framing members.
Don(resqcapt19)
_________________________
Don(resqcapt19)
Top
#77207 - 05/14/01 08:53 AM Re: Wires per hole??
wayne Offline
Member
Registered: 04/04/01
Posts: 54
Loc: NC
Sparky,
That is a good One.

That would Depend On the size of the hole.We would still consider art 300-4 in application of this method.

Wayne
Top
#77208 - 05/14/01 09:30 AM Re: Wires per hole??
sparky66wv Offline
Member
Registered: 11/17/00
Posts: 2232
Loc: West Virginia
I've mentioned before in another thread (there ought to be a law) that I'd like to see a requirement for bored-hole fill similar to pipe fill. I use it as a rule of thumb when dealing with larger cable, (2" for 4/0 SE. 1-1/4" for #2 SE, etc.)

As far as #14 and #12 NM Cable, I go no less than 3/4" , usually 1".
_________________________
-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Top
#77209 - 05/14/01 12:39 PM Re: Wires per hole??
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
Virgil;
yes you did, and it's worthy of a thread's consideration.

to add to the Q,
what would qualify as 'bundled'

Top
#77210 - 05/14/01 02:23 PM Re: Wires per hole??
Anonymous
Unregistered

A bored hole through a 2"X4" seems to have a lot in common with a nipple especially if the wall is insulated too.

Do you mean that some people don't make a separate hole for each cable on minimum one-diameter spacings?
Top
#77211 - 05/14/01 02:37 PM Re: Wires per hole??
sparky66wv Offline
Member
Registered: 11/17/00
Posts: 2232
Loc: West Virginia
Quote:
Do you mean that some people don't make a separate hole for each cable on minimum one-diameter spacings?


If I did that I'd be making $3 an hour on bid jobs... but for cost-plus, that's OK!

Please don't tell me it's code to do so...is it? It'd make swiss cheese out of the homes I've wired. One hole in the center of the joist/stud/plate makes for less structural degradation.

Bundled cable derating is one of the most ignored codes around here to this day... heck I'm guilty of it I suppose...
_________________________
-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Top
#77212 - 05/14/01 03:10 PM Re: Wires per hole??
Anonymous
Unregistered

Quote:
Please don't tell me it's code to do so...is it?


Of course it is legal to do so...


I can't speak to structural degradation, but I can't imagine how Swiss cheese is worse than a big whole. My gut feeling is that a bunch of half inch holes a half inch apart cause less weakening than a single large hole.

I've pulled NM out of joists where the holes were sized and shaped almost exactly to the oval shape of the cable.

Of course, 12-3-G fills a round hole nicely.

Let's just say that I lean toward Swiss cheese as the preferable way. I think so long as I'm leaving 60% there, it's structurally safe.
If you are making a single hole up to 1.5", I wouldn't object, especially if you are restoring it with steel.

Perhaps you need a faster drill or a sharper bit.

It's easier to trace wires through Swiss cheese than in a bundle, but a little harder to protect with plates.

No derating in Swiss cheese...
Top
#77213 - 05/14/01 03:56 PM Re: Wires per hole??
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
Myself,
There are probably few people outside of our trade that appreciate our's as having any asthetic value, but i just like a neat job.

if i do a complete building, i like to wire for expansion. So when it comes to wood i usually arrange via chalkline 3 to 4 1 1/2" or 2" runs back to the panel, possibly more closer to the panel. First i ask the carpenters, they are responsible for load bearing, etc. The time i take to do this pays off. I have found a self-feed and right angle works best, having all holes at an angle tends to work the wires thru hard.

All the runs are pulled easily, they occupy on average 1/3 to maybe 1/2 of the hole diameter, always room for that future sparky.

All runs starting from the panel fan out neatly, which looks good as an end result.

Top
#77214 - 05/14/01 04:07 PM Re: Wires per hole??
sparky66wv Offline
Member
Registered: 11/17/00
Posts: 2232
Loc: West Virginia
I believe the derating factor for 1" holes dead center of the framing member to have about a 4% decrease in structural integrity. 1/2" holes would be 3%. If they are not dead center, then up to 30% derating of the load carrying ability of the member must be assumed. I was told this by a P.E. I worked for, so I can't back up its accuracy. So it's kinda moot.

I guess the important thing is to have them dead center.

I don't put more than three cables in one hole under any circumstances, just a rule of thumb.

Quote:
$3 an hour

I should mention that I tend to "exaggerate for clarity" if that makes any sense. In today's sensationalized world, sometimes it's hard to get a point across without going to the extreme!

[This message has been edited by sparky66wv (edited 05-14-2001).]
_________________________
-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6775
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 85 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals