#77115 - 04/27/01 07:39 AM PVC with rigid straps
sparky66wv Offline
Member
Registered: 11/17/00
Posts: 2232
Loc: West Virginia
Can one use metal pipe straps with PVC conduit?

I see this a lot, and I was wondering.

Something tells me "no", but I've haven't found it in or near 347-5 through 9...
_________________________
-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Top
2017 / 2014 NEC & Related Books and Study Guides
#77116 - 04/27/01 12:13 PM Re: PVC with rigid straps
Bill Addiss Offline
Member
Registered: 10/07/00
Posts: 3875
Loc: NY, USA
'66,

I've never heard anything against using them. I would consider using them if I needed strong support and corrosion was not a concern. They would have to be the right size which would be for rigid (GRC) trade sizes not thinwall (Emt) sizes.

Was there something that you didn't like about using metal straps?


Bill
Top
#77117 - 04/27/01 05:42 PM Re: PVC with rigid straps
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
Well no!
I did a 400A 500 cu kcmil 3ph riser in 4" Sch 80 a while ago. Used beeline & 4" conduit clips every 24" .
The steel clips do not allow for the expansion of pvc, and are not listed for it's use.
But the plastic clips are whimpy, and this riser's 4-500's wieghed out to more than they are rated for!
Me....I'd rather see the pvc pull apart than fall off the building


[This message has been edited by sparky (edited 04-27-2001).]
Top
#77118 - 04/27/01 06:06 PM Re: PVC with rigid straps
sparky66wv Offline
Member
Registered: 11/17/00
Posts: 2232
Loc: West Virginia
I've always preferred using metal straps, but lately I've been learning a lot about a few of my assumptions about the NEC, and I had a feeling there was something hiding somewhere to prevent their use if they manufactured PVC straps.

Sparky has a good point about the expasion thing... I usually use 1 hole GRC straps...
Any difference here?
_________________________
-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Top
#77119 - 04/28/01 03:35 AM Re: PVC with rigid straps
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
Virgil;
try the 'quick-clips' for the small stuff. they live up to their name, quick...snap your pipe right in, comes out easy if needed, maintains the 1/4" standoff in wet/damp locations. I snap a line first....

Top
#77120 - 04/28/01 05:14 AM Re: PVC with rigid straps
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
I got called on metal straps once @ the beach because of the salt air, but can't imagine why they would cause a problem elsewhere. The code requires expansion joints where more than 1/4" of linear expansion is expected, and the diametric expansion can't be all that great. And yes, those PVC straps are whimpy.
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (HotLine1), 111 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals