The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
22 minutes 4 seconds ago
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
sparkyinak 9
Texas_Ranger 8
Potseal 6
Who's Online
2 registered (LongRunner, sparkyinak), 94 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#77105 - 04/25/01 04:29 AM NM Cable feeding outdoor Spa Disconnect
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
680-40 regarding outdoor spas refers back to 680 Parts A & B. 680-25(d) states that panelboards and disconnects when installed (and 680-12 requires that one always be installed) must have EGC that is insulated and installed in a choice of raceways. On the interior of a building, ENT(smurf tube) is acceptable. There is no exception as in 680-25(c),Motors, that would allow NM cable,(one of the wiring methods in Chap.3)to be used inside a one-family dwelling however, I repeatedly see this installed on the inside portion of the ckt. Thoughts?

Top
2014 / 2011 NEC & Related Books and Study Guides
#77106 - 04/25/01 10:32 AM Re: NM Cable feeding outdoor Spa Disconnect
David Offline
Junior Member

Registered: 04/23/01
Posts: 5
680-25(c)
Last Paragraph says that you can use a cable that has a ground insulated or covered by the outer sheath, I think that would include NM cable as long as it is copper and not smaller than # 12
_________________________
David

Top
#77107 - 04/25/01 12:09 PM Re: NM Cable feeding outdoor Spa Disconnect
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
David,
I am aware that 680-25(c) allows NM for motors. I am referring to 680-25(d)which also mentions disconnects along with panelboards. I see no reason to allow NM on the interior of a building to feed the disconnect required by 680-12.

Top
#77108 - 04/25/01 04:11 PM Re: NM Cable feeding outdoor Spa Disconnect
Glenn Offline
Member

Registered: 01/17/01
Posts: 78
680-25(d)(1) also notes between the service equipment and an EXISTING remote panelboard.

Does the installation meet or is required to meet that?

Glenn

Top
#77109 - 04/25/01 09:55 PM Re: NM Cable feeding outdoor Spa Disconnect
David Offline
Junior Member

Registered: 04/23/01
Posts: 5
Sorry Redsy,
I should have read your post a little closer
_________________________
David

Top
#77110 - 04/26/01 03:40 AM Re: NM Cable feeding outdoor Spa Disconnect
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
This is no particular installation. I have seen a few like this. They are new Spas with
disconnects mounted nearby, as required. NM cable feeds the disco, then PVC conduit goes on to feed the spa. I believe that 680-25(d)requires a raceway with an insulated ground to feed and ground the disconnect, even though it is fed from the inside of residences.

Top
#77111 - 04/26/01 05:43 AM Re: NM Cable feeding outdoor Spa Disconnect
Glenn Offline
Member

Registered: 01/17/01
Posts: 78
Redsy, on your post of 04-25-2001 03:09PM,

- - - 680-25(c) allows NM for motors - -.

I do not read the first paragraph of 250-25(c) to allow NM to the motor.

In general, I read 680-25 to allow an EXISTING installation using from service to a sub-panel when with-in the building.

But, to the motor under ANY condition, the EGC is to be INSULATED and in ONE OF THE RACEWAYS (or type MC cable) LISTED IN 680-25(c) ist paragraph. NM is not one of that list.

Glenn

Top
#77112 - 04/26/01 06:57 AM Re: NM Cable feeding outdoor Spa Disconnect
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
 Quote:
Originally posted by Glenn:
Redsy, on your post of 04-25-2001 03:09PM,

- - - 680-25(c) allows NM for motors - -.

I do not read the first paragraph of 250-25(c) to allow NM to the motor.

In general, I read 680-25 to allow an EXISTING installation using from service to a sub-panel when with-in the building.

But, to the motor under ANY condition, the EGC is to be INSULATED and in ONE OF THE RACEWAYS (or type MC cable) LISTED IN 680-25(c) ist paragraph. NM is not one of that list.

Glenn

Glenn,
The last paragraph of 680-25(c) allows an insulated OR covered ground, including any Chapt. 3 wiring method, for pool motors on the interior of a one-family dwelling. No such allowance exists in 680-25(d) regarding panelboards or disconnects. That was my original point. (Why do I see so many spa disconnects fed with NM cable? Seems like a violation to me.)

Top
#77113 - 04/26/01 06:28 PM Re: NM Cable feeding outdoor Spa Disconnect
Bill Addiss Offline
Member

Registered: 10/07/00
Posts: 4196
Loc: NY, USA
Redsy,

If the Spa was located indoors it could be wired with NM. What does that tell us about intent?

It is difficult to understand sometimes why things are written the way they are. Have you looked in any Handbooks as to what the intent is?

Bill

Top
#77114 - 05/11/01 05:31 AM Re: NM Cable feeding outdoor Spa Disconnect
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
Bill,
The handbook I own doesn't clarify.

[This message has been edited by Redsy (edited 05-11-2001).]