#77085 - 04/20/01 07:52 AM Code Enforcement Overkill?
Pete Offline
Junior Member
Registered: 04/20/01
Posts: 1
Built a metal building, with office inside with metal studs. No wood anywhere. Bldg & studs are grounded. Each receptacle has its own grounding lead. Our code enforcement inspector says each junction box must also have a grounding lug. Further, any rigid metal conduit with more than 3 load carrying conductors, conductors must be derated. So, if a 2" conduit has 4 conductors, the wire must be oversized. I'd appreciate comments.
Top
2017 / 2014 NEC & Related Books and Study Guides
#77086 - 04/20/01 08:03 AM Re: Code Enforcement Overkill?
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
Pete,
250-148(a) requires the EGC to be connected to the box. Table 310-15(b)(2)(a) requires derating of conductors for more than 3 current carrying conductors. Remember that is you are using THHN you can use the 90°C ampacity for derating purposes.
Don(resqcapt19)
_________________________
Don(resqcapt19)
Top
#77087 - 04/20/01 03:47 PM Re: Code Enforcement Overkill?
Tom Offline
Member
Registered: 01/01/01
Posts: 1044
Loc: Shinnston, WV USA
Pete,

Don's reply is right on the money. With THHN insulation in a dry location, you usually don't have a derating problem (at least in the smaller sizes) until you get to the 10th conductor.

Tom
_________________________
Few things are harder to put up with than the annoyance of a good example.
Top

Member Spotlight
Member Since: 08/22/05
Posts: 44
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 68 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Stack, Scotto, Freecrowder, clee512, Jdscott2005

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals