ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#77071 - 04/20/01 04:29 AM yet another Grounding Q
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
I would like to install a simple service in GRC pipe. Can i install the GEC from the meter in this pipe to gain entry into the dwelling?

got code?
Top
2017 / 2014 NEC & Related Books and Study Guides
#77072 - 04/20/01 06:51 AM Re: yet another Grounding Q
Mike Offline
Member
Registered: 02/21/01
Posts: 62
Yes. You can install the GEC in the same conduit as the service entrance conductors.
See article 230-7, exception No. 1.
Top
#77073 - 04/20/01 09:28 AM Re: yet another Grounding Q
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
Thanks Mike,

do you feel there are conflictions in 250 ?


i am interested in point of view here,

(for those posters that see my repetitive grounding inquires)
Top
#77074 - 04/20/01 01:22 PM Re: yet another Grounding Q
Glenn Offline
Member
Registered: 01/17/01
Posts: 75
Be sure to abide by 250-64(e) for each metal enclosure that the GEC passes through.

Glenn
Top
#77075 - 04/20/01 03:42 PM Re: yet another Grounding Q
Tom Offline
Member
Registered: 01/01/01
Posts: 1044
Loc: Shinnston, WV USA
Sparky,

I'll give you one of the violations that I cite in a service of this nature. I save this one for the folks who give me a hard time about correcting other violations of a serious nature. See 310-3, which requires conductors #8 & larger to be stranded if installed in raceways.

Tom
_________________________
Few things are harder to put up with than the annoyance of a good example.
Top
#77076 - 04/20/01 05:21 PM Re: yet another Grounding Q
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
hmmmm,
i'm tying to think of the last time i saw or used larger solid wire! I'd have to agree with that code Tom, it's a bear to put in pipe, at least of any length.

anyways, the GEC discussions always seem to incite the 'lightning' angle. Do you guys see any related problems here?

Top
#77077 - 04/20/01 05:32 PM Re: yet another Grounding Q
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
Tom,
Look at the exception to 310-3 and then look at 250-62. The exception says "as permitted or required elsewhere in this code". 250-62 permits the GEC to be a soild conductor without a size restriction.
Don(resqcapt19)
_________________________
Don(resqcapt19)
Top
#77078 - 04/20/01 06:12 PM Re: yet another Grounding Q
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
ok, let's go there!

Let's install a 200A simple meter, GRC down JB in thru sill plate, beat a #4 cu solid thru it( just to be difficult) bonding bushings at both pipe ends. GEC enters panel , has to bond at the pipe end entering, make to the term strip the MBJ is at, then exit the panel ( not sure how to bond there?) and down to G-rods, onto h20 pipe.

i'm thinking this may be nec compliant,yet electrically flawed in the nec's intent for a GEC
Top
#77079 - 04/21/01 06:46 AM Re: yet another Grounding Q
Tom Offline
Member
Registered: 01/01/01
Posts: 1044
Loc: Shinnston, WV USA
Don,

You're absolutely correct. I'll have to delete this one from my list.

Tom
_________________________
Few things are harder to put up with than the annoyance of a good example.
Top
#77080 - 04/21/01 06:14 PM Re: yet another Grounding Q
zapped1012 Offline
Junior Member
Registered: 04/18/01
Posts: 6
Loc: honesdale,pa
sparky, why do you want to do it the hard way? you only need to bond the grc at one end. either at the meter socket or main panelboard. then #6 to the rod and #4 to the water pipe from the panelboard. our utility here does not the gec in the meter socket.
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 10/07/00
Posts: 3417
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 35 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals