The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Yesterday at 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 170 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#77071 - 04/20/01 04:29 AM yet another Grounding Q
sparky Offline
Member

Registered: 10/18/00
Posts: 5545
I would like to install a simple service in GRC pipe. Can i install the GEC from the meter in this pipe to gain entry into the dwelling?

got code?

Top
2014 / 2011 NEC & Related Books and Study Guides
#77072 - 04/20/01 06:51 AM Re: yet another Grounding Q
Mike Offline
Member

Registered: 02/21/01
Posts: 65
Yes. You can install the GEC in the same conduit as the service entrance conductors.
See article 230-7, exception No. 1.

Top
#77073 - 04/20/01 09:28 AM Re: yet another Grounding Q
sparky Offline
Member

Registered: 10/18/00
Posts: 5545
Thanks Mike,

do you feel there are conflictions in 250 ?


i am interested in point of view here,

(for those posters that see my repetitive grounding inquires)

Top
#77074 - 04/20/01 01:22 PM Re: yet another Grounding Q
Glenn Offline
Member

Registered: 01/17/01
Posts: 78
Be sure to abide by 250-64(e) for each metal enclosure that the GEC passes through.

Glenn

Top
#77075 - 04/20/01 03:42 PM Re: yet another Grounding Q
Tom Offline
Member

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
Sparky,

I'll give you one of the violations that I cite in a service of this nature. I save this one for the folks who give me a hard time about correcting other violations of a serious nature. See 310-3, which requires conductors #8 & larger to be stranded if installed in raceways.

Tom
_________________________
Few things are harder to put up with than the annoyance of a good example.

Top
#77076 - 04/20/01 05:21 PM Re: yet another Grounding Q
sparky Offline
Member

Registered: 10/18/00
Posts: 5545
hmmmm,
i'm tying to think of the last time i saw or used larger solid wire! I'd have to agree with that code Tom, it's a bear to put in pipe, at least of any length.

anyways, the GEC discussions always seem to incite the 'lightning' angle. Do you guys see any related problems here?


Top
#77077 - 04/20/01 05:32 PM Re: yet another Grounding Q
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
Tom,
Look at the exception to 310-3 and then look at 250-62. The exception says "as permitted or required elsewhere in this code". 250-62 permits the GEC to be a soild conductor without a size restriction.
Don(resqcapt19)
_________________________
Don(resqcapt19)

Top
#77078 - 04/20/01 06:12 PM Re: yet another Grounding Q
sparky Offline
Member

Registered: 10/18/00
Posts: 5545
ok, let's go there!

Let's install a 200A simple meter, GRC down JB in thru sill plate, beat a #4 cu solid thru it( just to be difficult) bonding bushings at both pipe ends. GEC enters panel , has to bond at the pipe end entering, make to the term strip the MBJ is at, then exit the panel ( not sure how to bond there?) and down to G-rods, onto h20 pipe.

i'm thinking this may be nec compliant,yet electrically flawed in the nec's intent for a GEC

Top
#77079 - 04/21/01 06:46 AM Re: yet another Grounding Q
Tom Offline
Member

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
Don,

You're absolutely correct. I'll have to delete this one from my list.

Tom
_________________________
Few things are harder to put up with than the annoyance of a good example.

Top
#77080 - 04/21/01 06:14 PM Re: yet another Grounding Q
zapped1012 Offline
Junior Member

Registered: 04/18/01
Posts: 6
Loc: honesdale,pa
sparky, why do you want to do it the hard way? you only need to bond the grc at one end. either at the meter socket or main panelboard. then #6 to the rod and #4 to the water pipe from the panelboard. our utility here does not the gec in the meter socket.

Top