#77034 - 04/14/01 01:07 PM 230-79 (b)
Don'tKnowEverythingYet Offline
Member
Registered: 03/18/01
Posts: 22
Loc: Lakewood CA USA
This is the closest I got to finding the section that requires a sub panel in detached garages when there are more than two 20a circuits. (or is it one 20a circuit?)
I've heard about this requirement but can't find it in the '99 code. Does anybody know what section this would be in or is it just a California thing?
Top
2017 / 2014 NEC & Related Books and Study Guides
#77035 - 04/14/01 04:36 PM Re: 230-79 (b)
Tom Offline
Member
Registered: 01/01/01
Posts: 1044
Loc: Shinnston, WV USA
I don't believe that the NEC comes right out & states that a sub-panel is required. I also don't believe that the circuits are limited to 20 amps. You are limited to one circuit and it can be a multiwire circuit. 225-30

A disconnecting means is required (225-31) and it must be suitable for use as service entrance equipment 225-36, but there is an exception (of course) that applies to garages & outbuildings on residential property.

By applying all of the above & 225-33(b), you eventually come to the conclusion that a single multiwire circuit (could be 3 hots, I'm sure there are some individual houses that are served with 3 phase) is all that is allowed without going to a panel that would comply with 225-36.

I'm sure I've left something out, but for the life of me, can't figure out what it is. I'm sure others will jump in & cover any of my deficiencies.

Tom
_________________________
Few things are harder to put up with than the annoyance of a good example.
Top
#77036 - 04/18/01 01:48 PM Re: 230-79 (b)
wayne Offline
Member
Registered: 04/04/01
Posts: 54
Loc: NC
Your right Tom .
NEC does not come out and state the requirment. They kinda lead us into space sometimes.

As in most cases if there are more than two or three, 3wire circuits then a sub is usually installed.

For garage purpose's usually a multibranch circuit would cary what is needed it the garage.
Its a Cal thing,

Wayne
Top
#77037 - 04/18/01 04:26 PM Re: 230-79 (b)
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
this is the famous "what if" Q....
it goes in a repititous code loop, and usually ends up in a sub-panel.

Top
#77038 - 04/18/01 05:58 PM Re: 230-79 (b)
Glenn Offline
Member
Registered: 01/17/01
Posts: 75
Doesn't 215-2 also cover the feeder to the detached garage?
I do not see anything in 215-1 to limit 215 to the dwelling only.

How do you split up the loads without a sub panel ?

Glenn
Top
#77039 - 04/18/01 06:59 PM Re: 230-79 (b)
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
Glenn;
good post.
that would be a feeder, let's play with branch circuits just for fun!

Let's run 4 UF 12-2's
Let's terminate in a large metal switch box with 4 -20A single poles ( 230-80)
Then lets run a GEC from the box down to a few G-rods (250-32)

Now don't flame me thinking that I go around doing this sort of installation. It's rather that i go around having to deal with messes like this !
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (sparkyinak), 57 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals