The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
Today at 08:46 PM
International Wire Colour Codes
by Tjia1981
Yesterday at 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
0 registered (), 296 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#77034 - 04/14/01 01:07 PM 230-79 (b)
Don'tKnowEverythingYet Offline

Registered: 03/18/01
Posts: 22
Loc: Lakewood CA USA
This is the closest I got to finding the section that requires a sub panel in detached garages when there are more than two 20a circuits. (or is it one 20a circuit?)
I've heard about this requirement but can't find it in the '99 code. Does anybody know what section this would be in or is it just a California thing?

2014 / 2011 NEC & Related Books and Study Guides
#77035 - 04/14/01 04:36 PM Re: 230-79 (b)
Tom Offline

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
I don't believe that the NEC comes right out & states that a sub-panel is required. I also don't believe that the circuits are limited to 20 amps. You are limited to one circuit and it can be a multiwire circuit. 225-30

A disconnecting means is required (225-31) and it must be suitable for use as service entrance equipment 225-36, but there is an exception (of course) that applies to garages & outbuildings on residential property.

By applying all of the above & 225-33(b), you eventually come to the conclusion that a single multiwire circuit (could be 3 hots, I'm sure there are some individual houses that are served with 3 phase) is all that is allowed without going to a panel that would comply with 225-36.

I'm sure I've left something out, but for the life of me, can't figure out what it is. I'm sure others will jump in & cover any of my deficiencies.

Few things are harder to put up with than the annoyance of a good example.

#77036 - 04/18/01 01:48 PM Re: 230-79 (b)
wayne Offline

Registered: 04/04/01
Posts: 55
Loc: NC
Your right Tom .
NEC does not come out and state the requirment. They kinda lead us into space sometimes.

As in most cases if there are more than two or three, 3wire circuits then a sub is usually installed.

For garage purpose's usually a multibranch circuit would cary what is needed it the garage.
Its a Cal thing,


#77037 - 04/18/01 04:26 PM Re: 230-79 (b)
sparky Offline

Registered: 10/18/00
Posts: 5545
this is the famous "what if" Q....
it goes in a repititous code loop, and usually ends up in a sub-panel.

#77038 - 04/18/01 05:58 PM Re: 230-79 (b)
Glenn Offline

Registered: 01/17/01
Posts: 78
Doesn't 215-2 also cover the feeder to the detached garage?
I do not see anything in 215-1 to limit 215 to the dwelling only.

How do you split up the loads without a sub panel ?


#77039 - 04/18/01 06:59 PM Re: 230-79 (b)
sparky Offline

Registered: 10/18/00
Posts: 5545
good post.
that would be a feeder, let's play with branch circuits just for fun!

Let's run 4 UF 12-2's
Let's terminate in a large metal switch box with 4 -20A single poles ( 230-80)
Then lets run a GEC from the box down to a few G-rods (250-32)

Now don't flame me thinking that I go around doing this sort of installation. It's rather that i go around having to deal with messes like this !