#77025 - 04/13/01 10:18 AM Low-voltage Landscape Lighting Cable
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
It seems that table 300-5, Column 5 requires low-voltage landscape lighting cables to be buried 6". Article 110-3(b) requires equipment to be installed per manufcturers instructions.
Hadco(high-end fixtures, accessories,etc.)catalog states that the low voltage cable does not need to be buried,just covered with mulch, stones, etc. It recommends 4" burial when crossing lawns to avoid landscape tool damage. I once contacted Malibu, and was again told that the low voltage cable is not required to be buried. I say bury it 6" everywhere. What am I missing?
Top
2017 / 2014 NEC & Related Books and Study Guides
#77026 - 04/13/01 10:51 AM Re: Low-voltage Landscape Lighting Cable
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
1) 110-3(b) does not tell you that you must follow the manufacture's instructions. It tells you that you must follow any instructions that are part of the listing and labeling.
2) There are listed "relocatable" low voltage fixtures and would not think that that cable would have to be buried in that the fixtures are intended to be moved around.
3) If the installation is to be "permanent" then I would require the 6" as shown in Table 300-5.
4) If the low voltage lighting system is not a listed system, then the cable requires 24" of cover.
Don(resqcapt19)
_________________________
Don(resqcapt19)
Top
#77027 - 04/13/01 12:39 PM Re: Low-voltage Landscape Lighting Cable
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
Don;
i've been looking at a lot of instructions since you have brought 110-3(b) to my attention.
(Thank You)


Top

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 51 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 79
HotLine1 51
Ruben Rocha 29
gfretwell 25
Trumpy 20
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals