#76759 - 03/20/01 07:56 AM I'm curious...
Boscodog Offline
Member
Registered: 02/27/01
Posts: 13
Loc: Massachusetts
This is a purely hypothetical case that I'm posing.
Let's say you have an existing 20 amp branch circuit which you, for whatever reason, tap into somewhere with 14 gauge wire. So you downsize the fuse or circuit breaker in the panel to 15A to protect the 14 gauge wire.
Here is my question. Is there anything in the code that says you have to leave a note on the inside cover of the panel to explain why a 12 gauge wire in the panel has only 15A overcurrent protection? It seems to me that common sense indicates that you should. I'm just wondering if anyone knows offhand if the code has anything to say about this.
Top
2017 / 2014 NEC & Related Books and Study Guides
#76760 - 03/20/01 01:18 PM Re: I'm curious...
Bill Addiss Offline
Member
Registered: 10/07/00
Posts: 3875
Loc: NY, USA
Bosco,

It couldn't hurt labeling it in the panel. I don't know of any code rules requiring it though. It probably is not considered much of a concern as the ratings are close and if you look at Table 310-16 14awg wire (at 60C) has an allowable ampacity of 20 amps anyway - you just aren't supposed to use it as such.

Bill
Top
#76761 - 03/20/01 01:22 PM Re: I'm curious...
Tom Offline
Member
Registered: 01/01/01
Posts: 1044
Loc: Shinnston, WV USA
Reqired? No
Good idea? Yes

Evidently, this is not a real big safety issue, probably due to the lack of supporting evidence.

The same situation can arise when home run conductor sizes are increased to compensate for voltage drop.

Tom
_________________________
Few things are harder to put up with than the annoyance of a good example.
Top
#76762 - 03/21/01 04:55 PM Re: I'm curious...
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
I'm involved in a renovation , all the BX and K&T is being weeded out. But this is being done room by room. I am replacing all accessable with 12-2, but this still has some of the old circuitry connected until the renovation pushes ahead . So i have put all 12-2, 12-3 home runs on 15A. I have had to catalog this job as you have described.

Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 101 Guests and 13 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Stack, Scotto, Freecrowder, clee512, Jdscott2005

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals