#76643 - 03/04/01 09:22 PM GFI circuit question
GaryGnu Offline
Junior Member
Registered: 03/04/01
Posts: 7
Loc: MD, USA
On a house, I am installing a new receptable and 2 new lights outdoors. The receptacle will be tapped from a GFI receptacle from the basement of the house. Is it OK to wire the 2 outdoor lights on this same GFI circuit?
Top
2017 / 2014 NEC & Related Books and Study Guides
#76644 - 03/05/01 04:04 AM Re: GFI circuit question
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
Lights on a GFI can be a little tricky. This usually is only required where the light is listed for installation from a GFI, as in a shower recessed light.

I am stating this assuming you would supply your outdoor lights from the "load" rather than "line" side of said GFI.
Top
#76645 - 03/05/01 06:47 AM Re: GFI circuit question
GaryGnu Offline
Junior Member
Registered: 03/04/01
Posts: 7
Loc: MD, USA
Definitely coming from the load side of a receptacle 2 or 3 up the chain. Why is it tricky? The lights seem to work OK.
Top
#76646 - 03/19/01 10:14 AM Re: GFI circuit question
electrician02125 Offline
Member
Registered: 02/01/01
Posts: 89
Mr Gnu.

Call a licensed electrician. Your questions are all over these boards. You say you were a helper for six years. After 6 months I could answer all of the questions you've asked. Call a licensed electrician before you burn someones house down.

Nothing personal but this isn't a hobby.
CALL A LICENSED ELECTRICIAN.

Quote:
Originally posted by GaryGnu:
On a house, I am installing a new receptable and 2 new lights outdoors. The receptacle will be tapped from a GFI receptacle from the basement of the house. Is it OK to wire the 2 outdoor lights on this same GFI circuit?
Top
#76647 - 03/19/01 05:22 PM Re: GFI circuit question
sparky66wv Offline
Member
Registered: 11/17/00
Posts: 2232
Loc: West Virginia
When I was a journeyman in Wisconsin, I got a job working for an industrial outfit even though my experience was limited to residential. Jason, a 5th year apprentice, could run circles around me bending IMC and Rigid, and wiring motor controls, but when he was called upon to wire a three-way switch, he had to ask me how...! Which put things in perspective for me.

Any decent residential apprentice can wire a 3-way switch, but may know nothing of industrial work...

Any decent industrial apprentice can bend conduit, but may know nothing of residential work...

My hat is of to you GaryGnu, for not being afraid to ask.


Mr. electrician02125

The only problem I've had with having lights on GFCI is occasional nuisance tripping. Could you please enlighten us as to the hazards of this? Today, I installed a recessed light for a shower which was to be on a GFCI protection as per manufacturers instructions... perhaps Nutone would be interested in hearing your theories of these hazards...



[This message has been edited by sparky66wv (edited 03-19-2001).]
_________________________
-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6775
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 85 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals