#76620 - 03/01/01 09:36 AM bonding  
chuck  Offline
Member
Joined: Mar 2001
Posts: 10
decatur,il/usa
Where the code allows for installing a bonding conductor in mettalic conduit it states that the conduit must be bonded on both ends, question is if this is installed in mettalic conduit , attached to a metal building , does this reduce the requirement for bonding of the conduit?


2017 / 2014 NEC & Related Books and Study Guides

#76621 - 03/01/01 10:22 AM Re: bonding  
Glenn  Offline
Member
Joined: Jan 2001
Posts: 75
The bonding of the Grounding Electrode Conductor ( GEC) to each end of a metal raceway is required in 250 Part C, 250-64.

It appears the question has the GEC and the Equipment Grounding Conductor (EGC) inter-mixed.

Where a metal raceway encloses an EGC, I do not know where the NEC requires bonding each end of a metal raceway to the EGC. I also do not know where the NEC prohibits that practice.

250 Parts D, E, F, G, in general covers the equipment grounding required for systems less than 1000 volts.

Glenn


#76622 - 03/01/01 10:28 AM Re: bonding  
Glenn  Offline
Member
Joined: Jan 2001
Posts: 75
After re-read your question;

Each and every metal raceway enclosing the GEC must be bonded to the GEC at each end.

That would be Troughs, Conduits, Nipples, Junction Boxes, Switch and Meter enclosures etc.

Just by having the GEC metal raceway secured to a metal building structure would not accomplish this.

Glenn
Glenn


#76623 - 03/01/01 12:46 PM Re: bonding  
Bill Addiss  Offline
Member
Joined: Oct 2000
Posts: 3,875
NY, USA
Chuck,

Welcome to our Forum.
Others here can give you a more detailed answer I'm sure, but I'll give it a try. If you're talking about the Grounding Electrode Conductor (GEC) it must be bonded to the conduit so that it can work properly in the event of a Fault. If it is not bonded and there is a sudden rise in current flow on the conductor fields may be set up that will oppose the current flow and effectively "choke" it.

Anyone feel free to correct me or add to this.

Bill


#76624 - 03/01/01 01:45 PM Re: bonding  
chuck  Offline
Member
Joined: Mar 2001
Posts: 10
decatur,il/usa
Gentlemen, I am talking about a water pipe bond from the service eqipment to the water service as we require locally.


#76625 - 03/01/01 02:59 PM Re: bonding  
Bill Addiss  Offline
Member
Joined: Oct 2000
Posts: 3,875
NY, USA
Chuck,

Yes, that is what we are talking about if I understand it correctly. The conductor from the service that is connected to the water pipe runs through a metal conduit. this must be bonded at both ends as described in the code section mentioned. Over at the IAEI forum there was a recent thread with questions regarding types of clamps used and there are some pictures there too. take a look.
http://www.iaei.com/ubb/Forum1/HTML/000019.html

I hope this helps,

Bill



Member Spotlight
Lostazhell
Lostazhell
Bakersfield, CA (Originally Orange Co.)
Posts: 1,428
Joined: February 2004
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.017s Queries: 14 (0.003s) Memory: 0.7745 MB (Peak: 0.9188 MB) Zlib enabled. Server Time: 2017-03-27 08:40:51 UTC