The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Safety at heights?
by HotLine1
Yesterday at 08:51 PM
International Wire Colour Codes
by Texas_Ranger
Yesterday at 03:29 PM
Looking for older post
by Texas_Ranger
Yesterday at 03:22 PM
Last time to chat here
by Trumpy
01/20/17 11:41 PM
Unsafe Situations
by Trumpy
01/20/17 09:46 PM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
Admin 35
HotLine1 20
Ruben Rocha 17
gfretwell 16
Trumpy 15
Who's Online
0 registered (), 74 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#76620 - 03/01/01 05:36 AM bonding
chuck Offline
Member

Registered: 03/01/01
Posts: 10
Loc: decatur,il/usa
Where the code allows for installing a bonding conductor in mettalic conduit it states that the conduit must be bonded on both ends, question is if this is installed in mettalic conduit , attached to a metal building , does this reduce the requirement for bonding of the conduit?

Top
2017 / 2014 NEC & Related Books and Study Guides
#76621 - 03/01/01 06:22 AM Re: bonding
Glenn Offline
Member

Registered: 01/17/01
Posts: 78
The bonding of the Grounding Electrode Conductor ( GEC) to each end of a metal raceway is required in 250 Part C, 250-64.

It appears the question has the GEC and the Equipment Grounding Conductor (EGC) inter-mixed.

Where a metal raceway encloses an EGC, I do not know where the NEC requires bonding each end of a metal raceway to the EGC. I also do not know where the NEC prohibits that practice.

250 Parts D, E, F, G, in general covers the equipment grounding required for systems less than 1000 volts.

Glenn

Top
#76622 - 03/01/01 06:28 AM Re: bonding
Glenn Offline
Member

Registered: 01/17/01
Posts: 78
After re-read your question;

Each and every metal raceway enclosing the GEC must be bonded to the GEC at each end.

That would be Troughs, Conduits, Nipples, Junction Boxes, Switch and Meter enclosures etc.

Just by having the GEC metal raceway secured to a metal building structure would not accomplish this.

Glenn
Glenn

Top
#76623 - 03/01/01 08:46 AM Re: bonding
Bill Addiss Offline
Member

Registered: 10/07/00
Posts: 4196
Loc: NY, USA
Chuck,

Welcome to our Forum.
Others here can give you a more detailed answer I'm sure, but I'll give it a try. If you're talking about the Grounding Electrode Conductor (GEC) it must be bonded to the conduit so that it can work properly in the event of a Fault. If it is not bonded and there is a sudden rise in current flow on the conductor fields may be set up that will oppose the current flow and effectively "choke" it.

Anyone feel free to correct me or add to this.

Bill

Top
#76624 - 03/01/01 09:45 AM Re: bonding
chuck Offline
Member

Registered: 03/01/01
Posts: 10
Loc: decatur,il/usa
Gentlemen, I am talking about a water pipe bond from the service eqipment to the water service as we require locally.

Top
#76625 - 03/01/01 10:59 AM Re: bonding
Bill Addiss Offline
Member

Registered: 10/07/00
Posts: 4196
Loc: NY, USA
Chuck,

Yes, that is what we are talking about if I understand it correctly. The conductor from the service that is connected to the water pipe runs through a metal conduit. this must be bonded at both ends as described in the code section mentioned. Over at the IAEI forum there was a recent thread with questions regarding types of clamps used and there are some pictures there too. take a look.
http://www.iaei.com/ubb/Forum1/HTML/000019.html

I hope this helps,

Bill

Top