The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
51 minutes 42 seconds ago
International Wire Colour Codes
by Tjia1981
Today at 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 7
renosteinke 6
ghost307 6
Potseal 4
Who's Online
0 registered (), 277 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#76618 - 02/28/01 01:59 PM Grounding Conductor
jsb55 Offline
Junior Member

Registered: 02/28/01
Posts: 1
Loc: Roanoke, Virginia, USA
Section 250-91(b) (1996 NEC) allows the use of emt as the grounding conductor of a circuit. My question concerns whether the common type emt fittings will provide continuity or if some type of bonding connector should be used? What is normal in the industry?


2014 / 2011 NEC & Related Books and Study Guides
#76619 - 02/28/01 02:40 PM Re: Grounding Conductor
Tom Offline

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
EMT fittings will safely carry ground fault currents At least the steel ones will, some of the zinc die cast don't perform as well, mainly because the locknuts sometimes won't penetrate the paint on some boxes or fixtures.

Many electricians around here also install an equipment grounding conductor inside the conduit. We've all seen fittings that have loosened or have had the conduit pulled out & when that happens, there is no ground downstream from the break.

I personally pull in a seperate equipment ground in any conduit likely to get abused. I don't bother to do this with conduits that are 20 feet in the air, but once you drop down to 10 feet or so they can be easily damaged.