#76426 - 01/30/01 03:59 PM 15A Switches
sparky66wv Offline
Member
Registered: 11/17/00
Posts: 2232
Loc: West Virginia
Assuming #12 wire is being used, can one use 15 Amp snap switches on 20 Amp circuits assuming the load is less than 1440 Watts?
(80% of 15A @ 120V)

I don't like using #14 wire and I've always protected lighting circuits at 15A anyway; so can I put 20 Amp breakers in instead and still be code?

380-14a seems to point towards sizing for load rather than circuit protection...

But there's always a paragraph hiding in this book somewhere...
_________________________
-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Top
2017 / 2014 NEC & Related Books and Study Guides
#76427 - 01/30/01 04:33 PM Re: 15A Switches
Tom Offline
Member
Registered: 01/01/01
Posts: 1044
Loc: Shinnston, WV USA
Yes, you can put 15 amp switches on a 20 amp circuit, provided the load does not exceed 15 amps.

There is no reason that I know, other than controlling a motor, to "Derate" your switch to 80% (12 amps).
_________________________
Few things are harder to put up with than the annoyance of a good example.
Top
#76428 - 01/30/01 08:41 PM Re: 15A Switches
Bill Addiss Offline
Member
Registered: 10/07/00
Posts: 3875
Loc: NY, USA
'66,

Yes you can use 15 amp switches. I am kind of opposite in that I would prefer #14 on these 15 amp switches. It seems to me that getting the screw torque just right on (standard grade) 15 amp switches is tough. It's easy to overtighten and strip out the screws or if it's not tight enough you can watch the screws turn (loosen) as you push the device back into the box. I think 20 amp rated switches are a better match for #12 awg wire.

Bill
Top
#76429 - 02/23/01 11:53 PM Re: 15A Switches
sparky66wv Offline
Member
Registered: 11/17/00
Posts: 2232
Loc: West Virginia
Never had that problem with Leviton or Eagle brand devices...except for that time I used my DeWalt screw gun...live and learn!
_________________________
-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 48 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals