The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
Texas_Ranger 8
Trumpy 8
sparkyinak 7
Who's Online
1 registered (LongRunner), 206 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#76290 - 01/10/01 05:09 AM Pool Bonding
Bill Addiss Offline
Member

Registered: 10/07/00
Posts: 4196
Loc: NY, USA
Since I see We are on a Pool type train of thought and it does somehow make me feel warmer Let me try a question of my own.

We know (right?) that the pool itself and associated equipment need to be bonded together but it is not required to be connected to the equipment grounding conductor of the service or circuit supplying power. My question(s) is which way is best and does that change depending on location? Inside, outside, or other factors.
In other words, if it was just as easy to do it either way, which would be preferrable?and why?

Top
2014 / 2011 NEC & Related Books and Study Guides
#76291 - 01/10/01 02:53 PM Re: Pool Bonding
sparky Offline
Member

Registered: 10/18/00
Posts: 5545
That's a good one...... Without getting all coded out, i'll just say that the people who trained me taught me to ground the h___ out of everything, bond it all together, etc.

Top
#76292 - 01/10/01 04:04 PM Re: Pool Bonding
Bill Addiss Offline
Member

Registered: 10/07/00
Posts: 4196
Loc: NY, USA
Sparky,

That would be my guess, but there might be a downside to it I don't know about. The pump would already be bonded to Equipment ground through the grounding screw inside. Is another connection advantageous? I used to connect bond wire to the #12 insulated ground near the pump location. Suppose the connection was elsewhere, or if the Bond wire was connected directly to the panelboard? That would mean Parallel paths with different resistances. What about Lightning? Is it good to have a low resistance path back to the Buiilding?

Does anyone know if any of these are legitimate concerns?

Top
#76293 - 01/11/01 09:21 AM Re: Pool Bonding
sparky Offline
Member

Registered: 10/18/00
Posts: 5545
Ok, i'm in section B of art 680, there are a lot of changes here.....I'm still trying to figure the part where it does'nt bond to the supply?? Why would that be ?

Top
#76294 - 01/20/01 03:22 AM Re: Pool Bonding
sparky Offline
Member

Registered: 10/18/00
Posts: 5545
Ok, i think i see the difference....the panel serving the pool could be close to, or remote from it.

We are talking about a redundant bond, and a possible parrallel path created by it. This would be in addition to the equipment grounding conductor serving the pool circuitry.

Let me ask this, is there any condition in where the #8 pool bonding and the grounding eqiupment conductor of the branch(s) circuits serving the pool would NOT meet???

Top
#76295 - 01/20/01 05:21 AM Re: Pool Bonding
Bill Addiss Offline
Member

Registered: 10/07/00
Posts: 4196
Loc: NY, USA
Sparky,

I can see where someone replaced a pump and did not connect the ground wire, or wire was loose, lost that little green screw, broke the Ground prong off etc. These things happen all the time to other types of equipment.

That would break the link between the 2 paths