The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
Yesterday at 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
1 registered (HotLine1), 342 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#76164 - 12/20/00 09:42 AM Three Phase Panelboard
cinkerf Offline

Registered: 12/03/00
Posts: 81
Loc: Pittsburgh, Pennsysvania. ...
A 100A. three phase four wire mainlug only sub panelboard is fed from a single phase service panelboard 120/240V 200A within the same electric room. There is a three pole 100A. breaker in the single phase service panelboard protecting the three phase panelboard. The three phase four wire panel is used as a single phase panel. I've never seen this set up before. It's obviously an incorrect installation. I don't think a licensed electrican would ever perform such work. We are in the process of trying to locate the General Contractor to get the name of his sub contractor that did the work. Even if the three phase panel is used as a single phase panel proper balancing of loads would be difficult. I located section 210.11(b) to address that violation. Perhaps section 110.3(b) would also be applicable, "Installation and Use" of labeled equipment. Would anyone happen to know any other code sections that would apply to this obvious violation?

(Frank) cinkerf

2014 / 2011 NEC & Related Books and Study Guides
#76165 - 12/20/00 12:33 PM Re: Three Phase Panelboard
therain4 Offline

Registered: 12/18/00
Posts: 37
Loc: Dunmore,Pa. U>S.A.
article 384=16(f)forbids the use of three phase breakers on panelboards with less than three phases.

#76166 - 12/20/00 02:30 PM Re: Three Phase Panelboard
cinkerf Offline

Registered: 12/03/00
Posts: 81
Loc: Pittsburgh, Pennsysvania. ...
Thank you. That is EXACTLY the section I needed.