What is the best way to determine if the sheath of metal clad cable is suitable for equipment grounding. (Frank) cinkerf
Top
2017 / 2014 NEC & Related Books and Study Guides
#76126 - 12/14/00 04:42 PM Re: Metal Clad Cable
gpowellpec Offline
Member
Registered: 12/06/00
Posts: 128
Loc: Irving, Tx USA
Go to http://www.afcweb.com./ and enroll in their online learning program. It doesn't take long. AFC manufactures MC cable.
Top
#76127 - 12/14/00 05:52 PM Re: Metal Clad Cable
Bill Addiss Offline
Member
Registered: 10/07/00
Posts: 4196
Loc: NY, USA
It looks to me that MC armor by itself is not approved for Grounding. But AC armor w/strip is.

Table at: http://www.afcweb.com./groundcp.html
Top
#76128 - 12/15/00 04:28 AM Re: Metal Clad Cable
cinkerf Offline
Member
Registered: 12/03/00
Posts: 81
Loc: Pittsburgh, Pennsysvania. ...
I located section 250.18(8)(11) "The metallic sheath OR the combined metallic sheath and grounding conductors of type MC cable". It falls under Types of Equipment Grounding Conductors. If read word for word it seems as if the sheath of MC cable would be suitable for an equipment grounding method. (Frank) cinkerf
Top
#76129 - 12/15/00 04:31 AM Re: Metal Clad Cable
cinkerf Offline
Member
Registered: 12/03/00
Posts: 81
Loc: Pittsburgh, Pennsysvania. ...
Correction. That is section 250.118(8)(11)
Top
#76130 - 12/15/00 05:08 AM Re: Metal Clad Cable
Bill Addiss Offline
Member
Registered: 10/07/00
Posts: 4196
Loc: NY, USA
Frank,

You got me wondering what's going on then. If you look at AFC's FAQ page it lists some Qualities of the MC cable types


"The difference between HCF and MC cables (as manufactured by AFC Cable Systems) is the grounding capabilities of the cable assemblies.

Type HCF cable has a green grounding conductor plus the armor/bond wire combination, thereby providing redundant or isolated grounding capability. HCF is a Type AC cable and is manufactured in accordance with U.L. 4.

HCF cable may be installed in compliance with NEC 517 for health care facilities.

Type MC has only one equipment grounding means, a green grounding conductor. There are types of MC cable manufactured by AFC with two grounding conductors for additional grounding capability."

This is from page: http://www.afcweb.com./faq.html
and would seem to indicate that it is not approved for Grounding. I can see why you're questioning it.
Top
#76131 - 12/15/00 08:05 AM Re: Metal Clad Cable
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2209
Loc: IL
The UL White Book indicates that the interlocked metal tape sheath is NOT suitable as a grounding conductor and an insulated or bare EGC will be provided. It also says that "the sheath of the smooth or corrugated tube Type MC calbe or a combination of the sheath and a supplemental bare or green insulated conductor is suitable for use as the required EGC".
Don(resqcapt19)
_________________________
Don(resqcapt19)
Top
#76132 - 12/15/00 11:42 AM Re: Metal Clad Cable
cinkerf Offline
Member
Registered: 12/03/00
Posts: 81
Loc: Pittsburgh, Pennsysvania. ...
Don,
In the margin of section 250.118(8)(11) there is a verticle line which indicates a code change from the previous (1996) NEC. It does not specify smooth or interlocked metal sheath. It simply states type MC cable. I would have to agree with you based on your findings in the UL White Book.
(Frank) cinkerf
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Looking for older post
by sparkyinak
Today at 12:27 AM
License exam
by TRUE POWER
Yesterday at 11:33 PM
Members: Non-Members: Did you know?
by Admin
Yesterday at 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM

Who's Online
1 registered (HotLine1), 97 Guests and 15 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Tom
Tom
Member Since: 01/01/01
Posts: 1069

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals