#76115 - 12/13/00 10:25 AM Isolated ground receptacle
cinkerf Offline
Member
Registered: 12/03/00
Posts: 84
Loc: Pittsburgh, Pennsysvania. ...
A 120 volt 20 amp isolated ground receptacle is needed for computer equipment. The service panelboard is approx. 50 feet from computer equipment. A 12/3 metal clad cable is intended to be used. The green insulated wire will be used to connect directly to the green terminal of the isolated ground receptacle. The red insulated wire will be stripped bare and used to properly ground the metallic box. At the panelboard the red insulated conductor will be totally stripped bare and connected to the bonded neutral / grounding bar. There are no junction boxes between panelboard and isolated ground receptacle outlet box. Does anybody object to this installation? (Frank) cinkerf
Top
2017 / 2014 NEC & Related Books and Study Guides
#76116 - 12/13/00 01:37 PM Re: Isolated ground receptacle
rmiell Offline
Member
Registered: 11/09/00
Posts: 242
Loc: La Junta, Co. USA
Besides using the red wire for grounding? The main use of a isolated ground receptacle is to keep stray noise from getting onto the ground, and into the computer equipment. Run a 12/2 mc cable,with an insulated equipment grounding conductor, use fittings approved for grounding,attach the equipment grounding conductor to the metal box, run cable from load back to service panel, and call it good.

This will help by not allowing a path for noise to get onto the equipment grounding conductor.

Do not, like I have seen in some cases, add a seperate ground rod just for the computer equipment!

Good Luck!

Rick Miell
Top
#76117 - 12/13/00 02:38 PM Re: Isolated ground receptacle
Bill Addiss Offline
Member
Registered: 10/07/00
Posts: 3875
Loc: NY, USA
Rick,

You're assuming that the jacket of the MC cable is approved for grounding by itself. Is this true? I know that it was not at one time.
Top
#76118 - 12/13/00 03:21 PM Re: Isolated ground receptacle
pip Offline
Member
Registered: 12/13/00
Posts: 15
Loc: Little Elm,Tx
he is not using the jacket for a bare...read his post again. bill, would you explain the reasoning behind not running the seperate ground rod. I've ran many job where it was spec'd that way.
Top
#76119 - 12/13/00 03:55 PM Re: Isolated ground receptacle
Bill Addiss Offline
Member
Registered: 10/07/00
Posts: 3875
Loc: NY, USA
oops,

you're right Pip!
I thought Rick was still talking about Isolated Grounding Receptacles.

As to your question, there are others here better able to explain it than I, but I have also been involved in jobs where someone mistakenly specified different grounding schemes to eliminate noise. And, all I can say is that besides being against the code, they just didn't work. You need a good solid ground for several reasons. My experiences involved bonding of Transformers for Computer rooms in several Major retail chain stores where there was a difference in potential of about 29 volts Neutral to ground - (this gave them some problems with Cash registers also) After several weeks of work running new wiring (insulated grounds) and balancing circuits better the difference was down in the single digits, (would change somewhat with connected loads) but not gone. Finally they allowed me to bond the Transformer properly and the voltages almost vanished. So, just because it's specified doesn't mean that it's right or even beneficial.
Top
#76120 - 12/14/00 08:14 PM Re: Isolated ground receptacle
Scott35 Offline

Broom Pusher and
Member
Registered: 10/19/00
Posts: 2707
Loc: Anaheim, CA. USA
Sounds good, but instead of stripping the red, ID it with green tape [unless you are using non-metallic outlet boxes, but in that case, you would not need an equipment ground bond].

Attach the ground that will be for equipment bonding to the panel's enclosure. Isolate the other one until you get to the Grounding Electrode System for that particular system.

Scott.
_________________________
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Top
#76121 - 12/14/00 09:28 PM Re: Isolated ground receptacle
gpowellpec Offline
Member
Registered: 12/06/00
Posts: 127
Loc: Irving, Tx USA
Scott, maybe it should be pointed out that stripping, taping, and coloring a conductor in a multiconductor cable to mark it as an EGC is allowed only under conditions where it can be ensured that qualified persons will be doing the maintenance. (250-119(b))
Top
#76122 - 12/15/00 04:17 AM Re: Isolated ground receptacle
cinkerf Offline
Member
Registered: 12/03/00
Posts: 84
Loc: Pittsburgh, Pennsysvania. ...
In my original post I should of included that qualified persons will be doing the maintenance. After reading Scott's post I tend to agree with him. Instead of stripping the red conductor, ID with green tape would be better. (Frank) cinkerf
Top
#76123 - 12/15/00 01:43 PM Re: Isolated ground receptacle
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
sounds like an "isolated circuit" would do fine.....
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6778
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 53 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals