The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Would ELV branch circuits be a good idea?
by LongRunner
Today at 07:42 AM
100% breakers?
by Texas_Ranger
Today at 06:13 AM
Forum Software Upgrade coming soon...
by Trumpy
01/14/17 07:11 PM
Faricating Guards out if Lexan?
by Trumpy
01/14/17 07:09 PM
Dangerous DIY Advice
by Potseal
01/12/17 09:52 AM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
HotLine1 16
gfretwell 11
sparkyinak 10
ghost307 10
Webmaster 8
Who's Online
1 registered (brsele), 280 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#76110 - 12/09/00 06:34 PM 120V 400hz & 120V 60hz in the same raceway
Eclavea Offline
Junior Member

Registered: 12/09/00
Posts: 5
Loc: OKC
I'm wondering what are the regulations and disadvantages besides noise?
Can somebody help me out?

[This message has been edited by Eclavea (edited 12-09-2000).]

[This message has been edited by Eclavea (edited 12-09-2000).]
_________________________
Eclavea

Top
2014 / 2011 NEC & Related Books and Study Guides
#76111 - 12/10/00 05:42 AM Re: 120V 400hz & 120V 60hz in the same raceway
cinkerf Offline
Member

Registered: 12/03/00
Posts: 81
Loc: Pittsburgh, Pennsysvania. ...
NEC Article 300.3(c)(1) seems to permit such an installation. (Frank) cinkerf

Top
#76112 - 12/13/00 08:35 PM Re: 120V 400hz & 120V 60hz in the same raceway
doc Offline
Member

Registered: 11/25/00
Posts: 119
Loc: Texas
it is perfectly legal to run different voltages in the same conduit according to the NEC. Keep in mind that the NEC sets the minium standards.I will run 120 240 volts in same conduit but WILL NOT run 120 /240 with 277/440 you may know you did it but a lot of the unsuspecting do not know it and can be hurt or burn up equipment so if at all possible keep them apart
_________________________
MAY THE SUN SHINE ON YOUR FACE IN THE MORNING AND YOU AWAKE WITH A SMILE

Top
#76113 - 12/13/00 09:18 PM Re: 120V 400hz & 120V 60hz in the same raceway
Bill Addiss Offline
Member

Registered: 10/07/00
Posts: 4196
Loc: NY, USA
Make sure that you label the Neutrals somehow so that they will not be confused.

Top
#76114 - 12/27/00 08:56 PM Re: 120V 400hz & 120V 60hz in the same raceway
Eclavea Offline
Junior Member

Registered: 12/09/00
Posts: 5
Loc: OKC
Thanks for your input guys.