#75632 - 03/06/07 02:44 PM interlocking disconnects
jay8 Offline
Member
Registered: 07/28/05
Posts: 183
Loc: Vancouver, BC
Can anyone spec a disonnect with door interlock that also breaks the load via a contactor? Supply is three phase, 208 volt up to 600 volt, 100 to 200 amps. I am looking at a device that will prevent unauthorized persons from using the disconnect to break the load , and prevent them from opening an energized disconnect. thanks.
Top
Work Gear for Electricians and the Trades
#75633 - 03/06/07 04:54 PM Re: interlocking disconnects
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
Jay,
You can get field installed control circuit interlock switches for most disconnects. These interlock switches open before the main contacts of the disconnect and could be used to control a remote contactor.
Don
_________________________
Don(resqcapt19)
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (annemarie1), 67 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals