The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
1 registered (LongRunner), 221 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#75618 - 03/06/07 10:34 AM Cu or Al
Wizzie Electric Offline
Member

Registered: 01/16/06
Posts: 59
Loc: Maple Creek, Saskatchewan, Can...
I am replacing a panel 100A and the SEC is #2 Cu and is too short. The home owner wants to use up a roll of #2 Al he has. Is it acceptable to replace the #2 Cu between the panel and meter with #2 Al. And is the use of an antioxadent not required by the NEC (just wondering)
_________________________
Thanks.

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#75619 - 03/06/07 10:54 AM Re: Cu or Al
ITO Offline
Member

Registered: 11/26/06
Posts: 341
Loc: Texas
Depends on:

1) Local codes, some areas may not allow Al.
2) The insulation of the AL conductor (75°C or 90°C)READ T-310.16 for Ampacity. If you cant tell what type of wire it is, you should not use it.
3) If the lugs in the panel and meter are listed for AL use (probably yes, but check anyway)

...and "Nolox" is always a good idea with AL conductors and Lugs
_________________________
101° Rx = + /_\

Top
#75620 - 03/06/07 10:56 AM Re: Cu or Al
ITO Offline
Member

Registered: 11/26/06
Posts: 341
Loc: Texas
Also as an after thought, how long of run are we talking about?
_________________________
101° Rx = + /_\

Top
#75621 - 03/06/07 12:36 PM Re: Cu or Al
earlydean Offline
Member

Registered: 12/22/03
Posts: 749
Loc: Griswold, CT, USA
also, an antioxident is generally required by the manufacturer's installation instructions for aluminum conductors when the conductors are terminated in a damp location.
_________________________
Earl

Top
#75622 - 03/06/07 01:03 PM Re: Cu or Al
EV607797 Offline
Member

Registered: 10/25/06
Posts: 756
Loc: Fredericksburg, VA, USA
I just learned that anti-oxidant paste is NOT an NEC requirement after decades of working in the electrical field. This is the kind of thing you just assume when working with others. That's the value in sites like this.

Back to the original question, yes, I would use and trust AL cable if the panel and meter base lugs are rated for it (few aren't, at least not in the past 40 years or so). If aluminum is installed correctly, it's a highly-efficient conductor. I agree that there may be local restrictions on using it, but I have yet to encounter any AHJ that prohibits it. That's usually more of a customer or building owner-level restriction.

#2AL is permitted by the NEC for residential 100 amp services, which is actually an exception since it's really not rated to handle 100 amps under other circumstances.

[This message has been edited by EV607797 (edited 03-06-2007).]
_________________________
---Ed---

"But the guy at Home Depot said it would work."

Top
#75623 - 03/06/07 01:20 PM Re: Cu or Al
ShockMe77 Offline
Member

Registered: 06/11/05
Posts: 823
Loc: Rahway, New Jersey
Better make sure that whatever you use to connect the copper to aluminum is rated for connecting copper to aluminum. Ideal makes a wirenut specifically for this purpose. Maybe they also make a bug (split-bolt connector) for an application like this as well. Is there anyway you can talk this customer into replacing the conductors back to the meter pan?

[This message has been edited by ShockMe77 (edited 03-06-2007).]

Top
#75624 - 03/06/07 01:39 PM Re: Cu or Al
Wizzie Electric Offline
Member

Registered: 01/16/06
Posts: 59
Loc: Maple Creek, Saskatchewan, Can...
"Is there anyway you can talk this customer into replacing the conductors back to the meter pan?"

The plan is to replace them back to the meter pan.

The main breaker lugs are rated for Al and Cu. The run is about 6 feet.
_________________________
Thanks.

Top
#75625 - 03/06/07 02:12 PM Re: Cu or Al
ShockMe77 Offline
Member

Registered: 06/11/05
Posts: 823
Loc: Rahway, New Jersey
I thought for some reason that you were splicing the conductors because they were short. D'oh!

Top
#75626 - 03/06/07 09:39 PM Re: Cu or Al
DougW Offline
Member

Registered: 06/08/03
Posts: 1083
Loc: North Chicago, IL
As ITO said, I'd run it past the local AHJ first, but as long as you're within the conductor's ampacity, WTH.

Top
#75627 - 03/06/07 09:58 PM Re: Cu or Al
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
310.15(B)(6) says it is OK but if this house has a big load that cycles like an HVAC they might see a little extra dimming of the lights with the aluminum. 20 some feet of #2 might seem expensive to him now but how much will it cost if you have to come back to install it later?
_________________________
Greg Fretwell

Top