#75618 - 03/06/07 10:34 AM Cu or Al
Wizzie Electric Offline
Member
Registered: 01/16/06
Posts: 69
Loc: Maple Creek, Saskatchewan, Can...
I am replacing a panel 100A and the SEC is #2 Cu and is too short. The home owner wants to use up a roll of #2 Al he has. Is it acceptable to replace the #2 Cu between the panel and meter with #2 Al. And is the use of an antioxadent not required by the NEC (just wondering)
_________________________
Thanks.
Top
Work Gear for Electricians and the Trades
#75619 - 03/06/07 10:54 AM Re: Cu or Al
ITO Offline
Member
Registered: 11/26/06
Posts: 348
Loc: Texas
Depends on:

1) Local codes, some areas may not allow Al.
2) The insulation of the AL conductor (75°C or 90°C)READ T-310.16 for Ampacity. If you cant tell what type of wire it is, you should not use it.
3) If the lugs in the panel and meter are listed for AL use (probably yes, but check anyway)

...and "Nolox" is always a good idea with AL conductors and Lugs
_________________________
101° Rx = + /_\
Top
#75620 - 03/06/07 10:56 AM Re: Cu or Al
ITO Offline
Member
Registered: 11/26/06
Posts: 348
Loc: Texas
Also as an after thought, how long of run are we talking about?
_________________________
101° Rx = + /_\
Top
#75621 - 03/06/07 12:36 PM Re: Cu or Al
earlydean Offline
Member
Registered: 12/22/03
Posts: 751
Loc: Griswold, CT, USA
also, an antioxident is generally required by the manufacturer's installation instructions for aluminum conductors when the conductors are terminated in a damp location.
_________________________
Earl
Top
#75622 - 03/06/07 01:03 PM Re: Cu or Al
EV607797 Offline
Member
Registered: 10/25/06
Posts: 744
Loc: Fredericksburg, VA, USA
I just learned that anti-oxidant paste is NOT an NEC requirement after decades of working in the electrical field. This is the kind of thing you just assume when working with others. That's the value in sites like this.

Back to the original question, yes, I would use and trust AL cable if the panel and meter base lugs are rated for it (few aren't, at least not in the past 40 years or so). If aluminum is installed correctly, it's a highly-efficient conductor. I agree that there may be local restrictions on using it, but I have yet to encounter any AHJ that prohibits it. That's usually more of a customer or building owner-level restriction.

#2AL is permitted by the NEC for residential 100 amp services, which is actually an exception since it's really not rated to handle 100 amps under other circumstances.

[This message has been edited by EV607797 (edited 03-06-2007).]
_________________________
---Ed---

"But the guy at Home Depot said it would work."
Top
#75623 - 03/06/07 01:20 PM Re: Cu or Al
ShockMe77 Offline
Member
Registered: 06/11/05
Posts: 821
Loc: Rahway, New Jersey
Better make sure that whatever you use to connect the copper to aluminum is rated for connecting copper to aluminum. Ideal makes a wirenut specifically for this purpose. Maybe they also make a bug (split-bolt connector) for an application like this as well. Is there anyway you can talk this customer into replacing the conductors back to the meter pan?

[This message has been edited by ShockMe77 (edited 03-06-2007).]
Top
#75624 - 03/06/07 01:39 PM Re: Cu or Al
Wizzie Electric Offline
Member
Registered: 01/16/06
Posts: 69
Loc: Maple Creek, Saskatchewan, Can...
"Is there anyway you can talk this customer into replacing the conductors back to the meter pan?"

The plan is to replace them back to the meter pan.

The main breaker lugs are rated for Al and Cu. The run is about 6 feet.
_________________________
Thanks.
Top
#75625 - 03/06/07 02:12 PM Re: Cu or Al
ShockMe77 Offline
Member
Registered: 06/11/05
Posts: 821
Loc: Rahway, New Jersey
I thought for some reason that you were splicing the conductors because they were short. D'oh!
Top
#75626 - 03/06/07 09:39 PM Re: Cu or Al
DougW Offline
Member
Registered: 06/08/03
Posts: 1143
Loc: North Chicago, IL
As ITO said, I'd run it past the local AHJ first, but as long as you're within the conductor's ampacity, WTH.
Top
#75627 - 03/06/07 09:58 PM Re: Cu or Al
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
310.15(B)(6) says it is OK but if this house has a big load that cycles like an HVAC they might see a little extra dimming of the lights with the aluminum. 20 some feet of #2 might seem expensive to him now but how much will it cost if you have to come back to install it later?
_________________________
Greg Fretwell
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 05/03/03
Posts: 1137
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 93 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
KrmtFrg, Stack, Scotto, Freecrowder, clee512

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals