The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Today at 03:17 PM
Calling all Non-US members!! (Non-US only)
by aussie240
Yesterday at 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
sparkyinak 8
Texas_Ranger 8
Potseal 6
Who's Online
1 registered (Tony Moscioni), 213 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#75603 - 03/05/07 03:54 PM 320A Meter Pan
NJ_WVUGrad Offline
Member

Registered: 01/17/06
Posts: 48
Loc: Neptune, NJ, USA
(Sorry - posted this in the wrong area before)

Does anyone know any 320A Meter Pans that are specifically non residential?

I have only found residential models.

It is for an upgrade from a 200A service to a 400A at a Cell Tower Equipment Trailer.

The contract with the client specifies commercial/industrial type equipment only and I am trying to avoid any issues.

I personally would much rather install a CT cabinet, much easier to route conduit & shape 500kcm conductors in. But JCPL is fighting me on using a CT enclosure for a 400A Service.

Thanks for any help.

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#75604 - 03/05/07 06:09 PM Re: 320A Meter Pan
Fred Offline
Member

Registered: 04/30/01
Posts: 461
Loc: Straughn, IN 47387
What would be the difference between a residential and commercial 320A self contained meterbase?

Top
#75605 - 03/05/07 06:56 PM Re: 320A Meter Pan
SolarPowered Offline
Member

Registered: 07/05/04
Posts: 615
Loc: Palo Alto, CA, USA
I certainly understand that the customer wants to have high-quality components in his electrical system, and in particular wants to avoid the cheapo "contractor specials" often found is residential work. But I don't see the sense in automatically disqualifying something because it's used in residential work. For example, THHN wire is used in residential work in some cases; are you going to not use THHN wire because of that?

It seems to me that he is looking for a particular quality level. Is there perhaps a better way of specifying that that he will be happy with?




[This message has been edited by SolarPowered (edited 03-05-2007).]

Top
#75606 - 03/05/07 07:57 PM Re: 320A Meter Pan
frenchelectrican Offline

Member

Registered: 02/06/03
Posts: 938
Loc: Wi/ Paris France { France for ...
well one thing about the class 320 socket here in state of Wisconsin it have two verison either 320 [400 amp ] standard meter or we have 600 amp bolt on metering socket i don't have the website for other POCO for that one but my POCO do have one on the listing.

NJ_WVUGrad you may have to talk to the POCO for the listing of other approved meter socket sometime they do listed it

hope it help here

Merci , Marc
_________________________
Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)


Top
#75607 - 03/06/07 04:47 AM Re: 320A Meter Pan
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
To the best of my knowledge, I have not seen a JCP&L (GPU) meter pan rated over 200 amp, with the exception of the 320 for 'resi'.

First Energy (Parent Co.) website may have info you are looking for.

All 'over 200' comm jobs are CT jobs IMHO and experience.

John
_________________________
John

Top
#75608 - 03/06/07 09:54 AM Re: 320A Meter Pan
LK Offline

Member

Registered: 01/21/03
Posts: 1721
Loc: New Jersey
John, on the commercial we have used the 320, it's rated 320 continous 400 max, if he is running 320 continous IMO it might be a good idea to up the service.
I would not want that cell tower electric bill, with 320 continous.

Top
#75609 - 03/06/07 04:44 PM Re: 320A Meter Pan
NJ_WVUGrad Offline
Member

Registered: 01/17/06
Posts: 48
Loc: Neptune, NJ, USA
Thanks for the info Hotline

Getting a 400A CT through JCPL engineering is no problem, however getting it by the metering dept is another issue. They seem to be pushing the 320A meter pan for commercial use.

They are also making us a put a disocnnect ahead of the meter for all CT Cabinet jobs - Makes perfect sense to me and have no problem doing it - however they won't get off their a@# and print up a spec showing this.

Makes it hard to justify cost to the client, I get alot of "well contractor XYZ did it last week around the corner with no disco ahead of the meter, why do you say its needed"

Back to topic - the 320Amps is based on running all the radios at full call volume with the DC plant charging and both 5 ton AC's running.

I don't get the privilege (LOL) of performing load calcs - the client does that internally.
I stopped asking questions a long time ago

Top
#75610 - 03/06/07 07:00 PM Re: 320A Meter Pan
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
Les:
That's what this site is all about! As I said, I never used one. You are talking single phase, right?

NJ, the 'Cold Sequence' layout has been around for a while; PSE&G has it also.

Did you check out First Energy web??

John
_________________________
John

Top
#75611 - 03/06/07 08:05 PM Re: 320A Meter Pan
homer Offline
Member

Registered: 09/30/04
Posts: 68
Loc: Vancouver, WA, USA
www.b-line.com/product/metering/index.asp might have some information on meter sockets, although you probably have been searching on the Web already. Circle AW seems to have a large selection of meter enclosures.

Top
#75612 - 03/07/07 03:15 AM Re: 320A Meter Pan
NJ_WVUGrad Offline
Member

Registered: 01/17/06
Posts: 48
Loc: Neptune, NJ, USA
HotLine1

I know it has been around for 480V but I am justing getting into seeing it with 120V

MY main complaint is that by their own admission they have no printed material showing it. And it seems to be only loosely enforced at best - by only a few wiring inspectors

Top