The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm² flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
Texas_Ranger 8
Trumpy 8
sparkyinak 7
Who's Online
1 registered (LongRunner), 206 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 3 1 2 3 >
Topic Options
Rate This Topic
#75334 - 02/23/07 02:04 PM Generator Interlock ?
SparksNmore Offline
Member

Registered: 05/31/05
Posts: 16
Loc: KC KS
Just curious, what’s your thoughts on the Generator Interlocks?

They don't look fail safe to me.
http://www.interlockkit.com/

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#75335 - 02/23/07 03:21 PM Re: Generator Interlock ?
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
Had a similar set-up on UPS system panelboards, but it was "factory" installed, not an aftermarket 'add in'

Mechanical type interlocks have been around for a long time.

This seems like a good idea for a manual transfer setup. Now I ask....is the backfed cb bolted down (or clipped)???

John
_________________________
John

Top
#75336 - 02/23/07 04:28 PM Re: Generator Interlock ?
Roger Offline
Member

Registered: 05/18/02
Posts: 1779
Loc: N.C.
John,
 Quote:
Now I ask....is the backfed cb bolted down (or clipped)???
you're a trouble maker aren't you?


Roger


[This message has been edited by Roger (edited 02-23-2007).]

Top
#75337 - 02/23/07 04:55 PM Re: Generator Interlock ?
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
Roger:
Now that comment I would expect from Bob (Iwire). Now where is George Little??

John
_________________________
John

Top
#75338 - 02/26/07 10:06 AM Re: Generator Interlock ?
SteveFehr Offline
Member

Registered: 03/19/05
Posts: 1192
Loc: Chesapeake, VA
Even the high-dollar interlocks can be bypassed with a screwdriver. But we swear by them just the same- sure, I'd like to think nobody is stupid enough to close the tie breaker while the two halves of the switchboard are fed from separated sources, BUT...

So, yeah, I use a lot of interlocks but bypass a lot of interlocks during non-standard evolutions, too. Their purpose is not so much to force the "expert" into a certain sequence but moreso to protect the idiot from blowing something up. I don't have any experience with this brand, but it looks like it could easily save someone the cost of an MTS

Top
#75339 - 02/26/07 10:46 AM Re: Generator Interlock ?
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
Idiot proof is only good until the "better" idiot comes along.
_________________________
Greg Fretwell

Top
#75340 - 02/26/07 12:29 PM Re: Generator Interlock ?
Tom Offline
Member

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
I'll be giving one of these a try in the next month or so. This interlock offers a few advantages that I can see, namely, my customer does not have to make up his mind which circuits he wants on a separate panel. This interlock is also going to be handy due to a lack of space to mount another panelboard.

That better idiot mentioned above probably lives here in the Mountain State. We seem to lead the nation in the bad categories & trail in the good ones.

Tom
_________________________
Few things are harder to put up with than the annoyance of a good example.

Top
#75341 - 02/26/07 02:32 PM Re: Generator Interlock ?
HotLine1 Offline

Member

Registered: 04/03/02
Posts: 6804
Loc: Brick, NJ USA
Tom:
I doubt that you have the market cornered in 'better idiots'.

John
_________________________
John

Top
#75342 - 02/26/07 03:16 PM Re: Generator Interlock ?
Rewired Offline
Member

Registered: 01/01/06
Posts: 567
Loc: Hamilton, Ontario, Canada
No doubt someone is going to try and defeat the interlock! Why? Someone will probably figure they can TRY and lower their electric bill if they have their generator running at the same time their panel is being supplied off mains power OR they don't want to have their lights go out for that split second when they transfer back from gennie supply to mains supply.
Trust me I know people that would want to do that.. All I say is " good luck" to them!

A.D

Top
#75343 - 02/26/07 03:17 PM Re: Generator Interlock ?
JCooper Offline
Member

Registered: 12/30/02
Posts: 229
Loc: Kendall Park, NJ USA
Nothing is truly idiot proof, just idiot resistant