The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Today at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
Yesterday at 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Texas_Ranger 8
Trumpy 8
sparkyinak 7
Who's Online
0 registered (), 202 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#75226 - 02/17/07 04:44 PM Protection for wire derated.
Cinner Offline
Member

Registered: 12/01/04
Posts: 77
Loc: Kelowna, B.C., Canada
If you are derating wire due to conduit fill(example - 4/0 derated to 3/0 ampacity) should the circuit breaker be sized to protect the new derated amapacity of the 4/0?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#75227 - 02/17/07 05:09 PM Re: Protection for wire derated.
RobbieD Offline
Member

Registered: 02/23/03
Posts: 238
Loc: Canada
No, stay with circuit breaker size and just increase the awg of the wire when you have to derate.




[This message has been edited by RobbieD (edited 02-17-2007).]

Top
#75228 - 02/17/07 05:13 PM Re: Protection for wire derated.
SteveFehr Offline
Member

Registered: 03/19/05
Posts: 1192
Loc: Chesapeake, VA
The derated ampacity cannot exceed the overcurrent protection. So, you either have to downsize the breaker or upsize the cable. Normally, it's the latter since the original breaker size is chosen for a reason, but using a smaller breaker is OK if circumstances allow.

Top
#75229 - 02/19/07 05:48 AM Re: Protection for wire derated.
ghost307 Offline
Member

Registered: 05/09/05
Posts: 884
Loc: Chicago Illinois USA
Huh?
Are you saying that I can't feed a 15 amp load with a 20 amp breaker using #8 wire???
...or did I read your post wrong?
_________________________
Ghost307

Top