The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/22/16 09:52 PM
International Wire Colour Codes
by Texas_Ranger
10/22/16 08:24 AM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 12
renosteinke 6
HotLine1 6
ghost307 5
Potseal 4
Who's Online
1 registered (Tjia1981), 212 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#75226 - 02/17/07 04:44 PM Protection for wire derated.
Cinner Offline

Registered: 12/01/04
Posts: 77
Loc: Kelowna, B.C., Canada
If you are derating wire due to conduit fill(example - 4/0 derated to 3/0 ampacity) should the circuit breaker be sized to protect the new derated amapacity of the 4/0?

Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#75227 - 02/17/07 05:09 PM Re: Protection for wire derated.
RobbieD Offline

Registered: 02/23/03
Posts: 238
Loc: Canada
No, stay with circuit breaker size and just increase the awg of the wire when you have to derate.

[This message has been edited by RobbieD (edited 02-17-2007).]

#75228 - 02/17/07 05:13 PM Re: Protection for wire derated.
SteveFehr Offline

Registered: 03/19/05
Posts: 1192
Loc: Chesapeake, VA
The derated ampacity cannot exceed the overcurrent protection. So, you either have to downsize the breaker or upsize the cable. Normally, it's the latter since the original breaker size is chosen for a reason, but using a smaller breaker is OK if circumstances allow.

#75229 - 02/19/07 05:48 AM Re: Protection for wire derated.
ghost307 Offline

Registered: 05/09/05
Posts: 881
Loc: Chicago Illinois USA
Are you saying that I can't feed a 15 amp load with a 20 amp breaker using #8 wire???
...or did I read your post wrong?