The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 198 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 3 1 2 3 >
Topic Options
Rate This Topic
#75175 - 02/15/07 05:45 AM Fluorescent Trouble
HCE727 Offline
Member

Registered: 11/11/05
Posts: 190
Loc: Delaware County, PA, USA
A switch controls a bank of 2x4 drop in, 277, 3 tube bi-pin fluorescent lights with electronic ballasts. One fixture, in the middle of the run is not working. The ballast was replaced, 2 new tubes are put in and it works, put the third tube in an the light goes out. The fixture is replaced with another from a different location. The third tube is put in and the light goes out. The switch is flipped a couple of times and all of the light come on. The switch is flipped again, the fixture and the one next to it go out. The original fixture is put in another location and works fine. What could it be?
_________________________
Hank

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#75176 - 02/15/07 06:55 AM Re: Fluorescent Trouble
Zapped Offline
Member

Registered: 10/01/02
Posts: 481
Loc: Huntington Beach, CA, USA
That's a good one.

First, I'd bypass the switch to see if that's the problem.

Then I'd do a voltage reading under load at the middle fixture to see if there is a bad connection somewhere causing a VD or intermittent power.

Then, I'd go through the lamp sockets and internal wiring of the fixtures to see if there is anything causing the short-circuit protection of the ballasts to activate. Get the fixture lit and then jiggle the lamp a few times to see if causes the fault/shutdown.

Good Luck!

Top
#75177 - 02/15/07 07:37 AM Re: Fluorescent Trouble
HCE727 Offline
Member

Registered: 11/11/05
Posts: 190
Loc: Delaware County, PA, USA
Voltage is ok, this fixture is in the middle of about ten lights that are daisy chained. All of the other lights are working.
_________________________
Hank

Top
#75178 - 02/15/07 07:38 AM Re: Fluorescent Trouble
frenchelectrican Offline

Member

Registered: 02/06/03
Posts: 938
Loc: Wi/ Paris France { France for ...
but i dont know if you knew this or not some ballast did have multi light level on the ballast so you may have to cycle the switch few time to get it all light up

i know one Advance ballast do this way

hit the switch all 3 tube will be on then hit again switch to 2 or 1 tube set up and again back to all 3

sorta of 3 way light bulb work so just a thought

the other thing is that some lumiaire if you have " remote " type check the ballast for max distance if too far it may not fire up not very well at all

Merci , Marc
_________________________
Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)


Top
#75179 - 02/15/07 11:59 AM Re: Fluorescent Trouble
HCE727 Offline
Member

Registered: 11/11/05
Posts: 190
Loc: Delaware County, PA, USA
Nope, not it
_________________________
Hank

Top
#75180 - 02/15/07 12:29 PM Re: Fluorescent Trouble
wendel Offline
Member

Registered: 08/07/04
Posts: 57
Are you using bulk tubes or name brand? Did you wipe the tube of any dirt/film. Is the fixture securely grounded? I've been fighting a similar battle with mixed success.

Top
#75181 - 02/15/07 03:58 PM Re: Fluorescent Trouble
HCE727 Offline
Member

Registered: 11/11/05
Posts: 190
Loc: Delaware County, PA, USA
The tubes are brand name, the tubes were never wiped down and the fixture is properly grounded.
_________________________
Hank

Top
#75182 - 02/15/07 05:14 PM Re: Fluorescent Trouble
jdo1942 Offline
Junior Member

Registered: 11/13/05
Posts: 32
Loc: st. louis, mo. usa
IS IT POSSIBLE THAT THE BANK OF LIGHTS THAT YOU ARE HAVING PROBLEMS WITH HAS VOLTAGE PROBLEMS? THERE MAY BE VOLTAGE DROP ISSUES DUE TO DISTANCE OR WIRE SIZE. DON'T FORGET ELECTRONIC BALLASTS GENERATE ALOT OF HARMONICS THAT MIGHT AFFECT THE CIRCUIT.

Top
#75183 - 02/15/07 05:20 PM Re: Fluorescent Trouble
HCE727 Offline
Member

Registered: 11/11/05
Posts: 190
Loc: Delaware County, PA, USA
Why is it the fixture in the middle and the one next to it, in a bank of about 10 lights. All of the lights are controlled by one switch. The other lights work fine. There is also another problem in another office in the same building, but on another floor.
_________________________
Hank

Top
#75184 - 02/16/07 05:17 AM Re: Fluorescent Trouble
Jps1006 Offline
Member

Registered: 01/22/04
Posts: 609
Loc: Northern IL
Are you lamping these while energized? I have read on certain fluorescent ballasts before "do not lamp while energized. Lamp will not properly light"

Is this switch rarely operated and left on overnight? Just a stab, but.... excersing the switch reset the ballast that was lamped live and the light next to it was just waiting for a reason not to come back on, it was close to its end of life.

Top