The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Parking lot pole light swap....
by HotLine1
10/23/16 09:39 AM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 12
HotLine1 7
renosteinke 6
ghost307 5
Potseal 4
Who's Online
1 registered (Tjia1981), 194 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#75114 - 02/14/07 07:49 AM Sheilded cable through nonbonded sleeve
Jps1006 Offline

Registered: 01/22/04
Posts: 609
Loc: Northern IL
I have a complex heat mat configuration for a custom bath that needs to use 3 mats on 1 t-stat. For one of the mats, I am going to run the lead through a wall at the floor to get into the room for the t-stat. Normally the tile guy sets the mat and can run as much as 12' lead around the perimeter of the heated area to get to the sleeve that gets the lead up the wall and to the t-stat.

The wire is made up of (2) insulated conductor that is wrapped with a braided ground to activate the GFI if the cable is faulted through. I'm wondering, would that allow me to stick a nonbonded 5" EMT sleeve through the wall since any induced voltage would travel down the braided ground?

Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#75115 - 02/14/07 09:28 PM Re: Sheilded cable through nonbonded sleeve
hbiss Offline

Registered: 12/16/03
Posts: 893
Loc: Hawthorne, NY USA
Seems you have both conductors in the cable (hot& neutral) so regardless of the "shield" induction would not be a problem.