The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 6 Guests and 1 Spider online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#7484 - 02/07/02 06:13 PM Testers
tmeg46 Offline
Member

Registered: 01/21/02
Posts: 10
Loc: Naples, Fl, USA.
Would like an opinion on testers. Pros and cons, on the following: 1) non-contact proximity tester. 2) Wiggy 3) A multi purpose (voltage, ohm, amprobe) type, digital or otherwise.
Do electricians, service or construction, use one over the other and which is best. I have my opinions (their like noses, right?) but would just like to hear from others.

Thanks, Tom

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#7485 - 02/07/02 07:41 PM Re: Testers
Bill Addiss Offline
Member

Registered: 10/07/00
Posts: 4196
Loc: NY, USA
Tom,

>> 1) non-contact proximity tester
My all-time Favorite Tool I wouldn't go to work without it.

Bill

Top
#7486 - 02/07/02 07:54 PM Re: Testers
George Corron Offline
Member

Registered: 05/16/01
Posts: 728
Loc: Lorton, Va USA
You realize though, that all those testers have their charms. Wiggies are light, nearly unbreakable (especially if you have one of the old metal ones ) Contact testers are nice, but....seen 'em fail. Analog testers you can see a capacitive "kick" as it leaves a circuit being tested, digital, nice and accurate, you often see the peak voltage (170) before it settles down to 120, now with digital do you want true or average readings, that also makes a difference and there are reasons for wanting both, WELL now that I've thoroughly confused the issue, I'll leave

Top
#7487 - 02/07/02 08:34 PM Re: Testers
Jim M Offline
Member

Registered: 08/10/01
Posts: 453
Loc: Chestertown, MD, USA
I just got a non-contact tester. I don't know what I did without it.

All of these meters have their uses. I have at least one of each along with 2 amp meters, one digital, one analog for cold weather.

Top
#7488 - 02/08/02 04:26 AM Re: Testers
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
I know many will say that you should not rely on them solely, but sometimes we get complacent. Non-contact testers have a serious, potentially deadly quirk. If a cable(particularly NM, which has a paper filler which retains moisture) has been exposed to moisture, they may not indicate voltage when ther is voltage present. My brother was installing an outdoor receptacle on a tail of NM that someone else had started a few weeks before. The non-contact tester did not beep. When he went to shorten the cable with his cutters, it sparked and tripped the breaker. If the cable had not been too long, he would have stripped it while kneling in damp grass, and probably would have been killed. Non-contact testers are a great device, but don't bet your life on them!
As far as others, Ideal has a Vol-Con Elite tester #61-092, that has a non-contact feature and a non solenoid vibrating feature, which is good for day-to-day use.
I like the fluke 89 IV DMM. It has lots of nice features.

[This message has been edited by Redsy (edited 02-08-2002).]

Top
#7489 - 02/08/02 06:35 AM Re: Testers
buddy Offline
Member

Registered: 09/11/01
Posts: 11
Along the lines of testers, is there a requirement that all testers have to be UL listed? Could you make your own tester and still be "legal"?

Top
#7490 - 02/08/02 04:39 PM Re: Testers
SPARKSALOT Offline
Member

Registered: 12/24/01
Posts: 29
Loc: Omak, WA, USA
I use a non contact tester for 120 stuff in "safe" situations. Where there may be higher voltages or I am outside or could be grounded somehow I use a fluke 23 or 87. I also sometimes use an Ideal voltage/continuity meter. I used to work for Shell oil and they required these or equivalent because of the inherent safety of not being able to have a selector in the wrong position. I have learned the value of that in the few times I have left my Flukes in current setting and hooked across 277v. Very fast way to get your attention.
Don

Top
#7491 - 02/08/02 05:22 PM Re: Testers
electure Offline

Member

Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
I carry both a Fluke T-5 and an old (25 yrs.)Square D "Wiggy" for checking if a circuit is dead. I use them both. Very often the Fluke high-impedance digital will show voltage on a circuit that's turned off, due to capacitance.
Also love my Fluke 36. RMS-AC/DC

Top
#7492 - 02/08/02 05:30 PM Re: Testers
Chris Rudolph Offline
Member

Registered: 05/01/01
Posts: 160
Loc: Winter Park,Fl USA
I carry both the proximity tester and a digital multimeter as well as an analog clamp on current meter.
One thing that I recommend is to test whatever instrument you use on a known powered up circiut before using it on the unknown.

Chris

Top
#7493 - 02/08/02 07:06 PM Re: Testers
CTwireman Offline
Member

Registered: 02/07/02
Posts: 839
Loc: Connecticut, USA
I use a non-contact all the time. I also use a Vol-con for checking continuity and grounds, and an Amprobe ACD-10 clamp-around DMM when I need accurate voltage and current readings.

The non-contact is nice because it fits in your tool belt or pocket, but its not very rugged.

The Vol-con is almost indestructible, as I've thrown it, dropped it and abused it and it still works.

Of course, always "test your tester" first, especially the non-contact.

So, I would say all 3 tester types are essential to have.
_________________________
Peter

Top