The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Today at 02:39 AM
Photo Upload Tutorial
by DanK
Yesterday at 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 282 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 8 1 2 3 4 5 6 7 8 >
Topic Options
Rate This Topic
#74752 - 02/04/07 08:43 AM # of conductors in conduit
kyelectric Offline
Member

Registered: 08/30/05
Posts: 64
No matter what the size of the conduit, you always have to derate the conductors accordingly when you have over 3. Correct? So, like most people think, "put a bigger size conduit in and you can pull more wires!" For instance, putting 1/2" EMT in limits the # of conductors that can be pulled because of it's size. But really, even if I put a 1" EMT conduit in I can fit more conductors in but I have to start derating at 4-7 conductors. So even if I put a 2" EMT conduit in and I could physically fit alot of #12 THHN conductors inside I would have to derate the #12 THHN to 80% of its ampacity when I reached 4-7 conductors. If this is not correct please advise. Thanks!

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#74753 - 02/04/07 09:00 AM Re: # of conductors in conduit
Roger Offline
Member

Registered: 05/18/02
Posts: 1779
Loc: N.C.
You are correct, it doesn't matter what size conduit you use, the derating requirements start with 4 current carrying conductors

Roger

Top
#74754 - 02/04/07 03:03 PM Re: # of conductors in conduit
Tom H Offline
Member

Registered: 01/31/05
Posts: 74
Loc: Milford, Ct, USA
Look in the code though, the normal use amperage and derateing amperage of some guages of wire are different. No code book here at home, but you derate from the higher amperage, still paying attenetion to the max amperage for that particular guage. If I remember correctly.

Code theory is so fun...

Top
#74755 - 02/05/07 09:40 AM Re: # of conductors in conduit
SteveFehr Offline
Member

Registered: 03/19/05
Posts: 1192
Loc: Chesapeake, VA
Are you talking small wires or large? For #12 THHN (90C), for instance, Table 310.16 allows 30A, but 240.4(D) restricts #12 to 20A maximum. For derating, though, you would use table 310.16, and would be able to put 7-9 #12 THHN conductors in a conduit before having to derate below 20A.

You do not have to count grounds for derating purposes, and may or may not have to count the neutral, depending what kind of circuit(s) you have. And I don't know if there is a code that explicely states it, but switched conductors (like in a 3-way switch) should only count as one conductor too, as only one will ever be considered a "conductor" at any given time.

Top
#74756 - 02/05/07 10:07 AM Re: # of conductors in conduit
SolarPowered Offline
Member

Registered: 07/05/04
Posts: 615
Loc: Palo Alto, CA, USA
Also note that you can put up to 20 CCC's in one pipe if you use #10 for 20A, and #12 for 15A. That approach is used a good deal in commercial work.

Top
#74757 - 02/05/07 01:24 PM Re: # of conductors in conduit
stevecheyenne Offline
Member

Registered: 11/29/06
Posts: 38
Loc: Yorba Linda, CA
Especially if you're upsizing the wire for voltage drop anyway.

Top
#74758 - 02/05/07 03:50 PM Re: # of conductors in conduit
electure Offline

Member

Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
Are you still having misunderstandings with your same piece of 2" conduit and the same plant engineer?
 Quote:
switched conductors (like in a 3-way switch) should only count as one conductor too,


That would apply only to the travellers. The switchleg conductor must be counted as a current carrying conductor.

[

[This message has been edited by electure (edited 02-05-2007).]

Top
#74759 - 02/05/07 04:13 PM Re: # of conductors in conduit
kyelectric Offline
Member

Registered: 08/30/05
Posts: 64
Electure, I explained to the plant engineer that the larger size conduit does not mean that I can fill it all the way up. He wants to use it for "future expansion" but I told him about the code making me derate the conductors after 4. Anyway, I did everything legally, they just ended up eating alot of wire cost because I had to upsize the #12's to #10's and the #10's to #8's. Thanks for the input!

Top
#74760 - 02/05/07 04:16 PM Re: # of conductors in conduit
kyelectric Offline
Member

Registered: 08/30/05
Posts: 64
SolarPowered, what do you mean by CCC's? Something...Circuit Conductors. I need to know more about this. Thanks!

Top
#74761 - 02/05/07 04:24 PM Re: # of conductors in conduit
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
CCC = current carrying conductor
_________________________
Don(resqcapt19)

Top