ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

Topic Options
Rate This Topic
#74705 - 02/02/07 07:34 AM operating cost?
Rob Offline
Member
Registered: 12/22/03
Posts: 15
Loc: New York
How do you determine operating cost of a 3 phase motor. 460 volt 15 amp.
My utility rate is .08 cents per kwh.
Is there a common formula?
Top
Work Gear for Electricians and the Trades
#74706 - 02/02/07 07:58 AM Re: operating cost?
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
Measure the actual amps drawn on each leg. Average. Multiply by 1.73. That's your amp load.

From there, it's the usual amps x volts x time x rate = electrical cost.

This will give you figures good enough to work with. Actual results will vary a bit, due to changes in load, power factor, harmonics, etc ... but the number you get will be close enough for budgeting.
Top
#74707 - 02/02/07 02:20 PM Re: operating cost?
JBD Offline
Member
Registered: 07/12/01
Posts: 599
Loc: WI, USA
One quick and dirty method is to estimate 1KVA of input power for each HP of output.

For a fully loaded motor you can use 1KW per HP. For lightly loaded motors use 1.1KW per HP instead.
Top

Member Spotlight
Member Since: 08/22/05
Posts: 44
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 45 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals