My neighbor has three new baseboard heaters and wanted me to install them. They are 208V and I told him that they cannot be used. From my understanding, 208V is 220V three-phase to ground.

Am I correct?

Thanks in advance, Doug.
Top
Work Gear for Electricians and the Trades
#7471 - 02/06/02 04:18 PM Re: 208V questions
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
Doug,
Are you sure that they are not dual rated 208/240? Most of them that I have seen are. The wattage is 25% less when on 208.
Don(resqcapt19)
_________________________
Don(resqcapt19)
Top
#7472 - 02/06/02 07:00 PM Re: 208V questions
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
The 208 that you refer to is the "high-leg" voltage to ground on a 240/120 volt 3 phase delta connected transformer secondary with on of the windings tapped at midpoint to provide 120 volts. The voltage of one of the phases, usually the "B" phase is about 208 and obviously should be avoided if connecting 120 volt equipment.
There is also a wye connected 208/120 3 phase system where all 3 phases are at 120 volts to ground.
Top
#7473 - 02/06/02 07:37 PM Re: 208V questions
dugmaze Offline
Member
Registered: 12/18/00
Posts: 45
Loc: St. Louis
No, I double checked and it is only 208V. So if all I have is 120V single phase or 220V two phase then I can't wire this up.
Top
#7474 - 02/07/02 04:04 AM Re: 208V questions
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
I would not use 208 heaters at 240 volt. But, most of the ones I've seen are dual rated. If they are not dual rated, have him get 240 volt heaters.
BTW, you probably do not have two-phase voltage. It is very uncommon these days. You must mean 240 volt single phase with a neutral. This is the standard residential system.
Top
#7475 - 02/07/02 05:21 AM Re: 208V questions
bobc Offline
Member
Registered: 02/05/02
Posts: 11
Loc: houston tx
Doug,

Three phase 208 is derived from a four wire

wye connected transformer configuration .

120 volts to neutral,208 phase to phase
Top
#7476 - 02/07/02 07:00 AM Re: 208V questions
dugmaze Offline
Member
Registered: 12/18/00
Posts: 45
Loc: St. Louis
Somebody must have bought these for a commercial building. Thanks for your help.
Top
#7477 - 02/07/02 04:02 PM Re: 208V questions
Steve Miller Offline
Member
Registered: 08/30/01
Posts: 325
Loc: Loudoun Cty, VA
Doing a little basic Ohm's Law here (ignoring the fact that this is AC not DC) you'll find that a 5000 watt (I just used this value for comparison) 208v unit draws 24 amps and has ~8.67 Ohms resistance. The same unit at 240v would draw ~28 amps and put out 6720 watts (R basically stays the same). Their life span will be real short.
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (cableguy619), 64 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals