#74465 - 01/22/07 05:27 PM Generator low voltage controls
sparkync Offline
Member
Registered: 10/17/02
Posts: 812
Loc: NC
I recently wired a 7 KW gas stand by generator. The flex that came with the generator had the low voltage control wiring running with the high voltage wiring. When I wired the disconnect for it I had to run the wiring in the same conduit also. Does generator wiring differ from normal wiring? I have another generator I am wiring up, and if permisable, it would be a whole lot more convenient to run it in the same conduit also. The control voltage on this one is 240 volt also, but there are two "remote status" leads that are 12 volt dc. The terminals for thes are also located in the disconnect with the 240 volt connections. I'm sorta confused here Thanks Steve...
Top
Work Gear for Electricians and the Trades
#74466 - 01/22/07 07:33 PM Re: Generator low voltage controls
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
As long as you make it class 1 compliant the "low voltage" can be there. basically you need to treat that LV as line voltage everywhere it goes.
_________________________
Greg Fretwell
Top
#74467 - 01/22/07 08:00 PM Re: Generator low voltage controls
Grover Offline
Member
Registered: 01/19/05
Posts: 109
Loc: Sebago, ME, USA
I've been confused by that also on several installations.....

Anybody got a code reference?

I've done it by the book (GeneratorRAC supplied), but checked my insurance and proceeded......

Grov
Top
#74468 - 01/22/07 08:53 PM Re: Generator low voltage controls
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
725.26(B)?
_________________________
Greg Fretwell
Top
#74469 - 01/23/07 03:36 AM Re: Generator low voltage controls
pauluk Offline
Member
Registered: 08/11/01
Posts: 7520
Loc: Norfolk, England
We have a similar situation with the British "code." Low-voltage control wires can be pulled into the same conduit as 240V so long as they are insulated to the higher voltage.
Top
#74470 - 01/23/07 09:40 AM Re: Generator low voltage controls
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
The other important consideration is the low voltage must be associated with controlling the line voltage equipment it shares a raceway with. This becomes a class 1 which basically follows all the chapter 3 rules.

You only get away with the relatively casual "low voltage" rules when this is class 2 and 3, current limited and effectively separated from line voltage conductors.
_________________________
Greg Fretwell
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6778
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (HotLine1), 61 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals