#74333 - 01/20/07 10:55 AM "back-stab" Connection Guts
wendel Offline
Member
Registered: 08/07/04
Posts: 55
Has anyone torn apart a receptacle and seen exactly how much contact surface area there is with the back-stab connection?

I don't want to open a can of worms but am curious if there's enough surface contact to prevent a hot spot from developing on the first receptacle when there's a load on the last in a series of receptacles.
Top
Work Gear for Electricians and the Trades
#74334 - 01/20/07 12:19 PM Re: "back-stab" Connection Guts
LK Offline
Member
Registered: 01/21/03
Posts: 1429
Loc: New Jersey
Shhhhh! Back stabs are great, if they stopped using them, a large percent of our service calls would dry up.
This week was a good example of the wonders of back-stabs, as soon as the tempeture snaps, the calls start comming in, yes the down stream load, will be on the first recpt.
Top
#74335 - 01/20/07 04:29 PM Re: "back-stab" Connection Guts
Obsaleet Offline
Member
Registered: 04/05/03
Posts: 362
Loc: Pa
Lk , I'm right with you. Stab in back 8 receptacles add 1 space heater on the last receptacle and Baaam!! 1 service call. Have you ever seen the voltage drop on the end?


Ob
_________________________
Choose your customers, don't let them choose you.
Top
#74336 - 01/20/07 05:37 PM Re: "back-stab" Connection Guts
colorado_sparky Offline
Member
Registered: 01/18/07
Posts: 10
Loc: Broomfield, CO USA
I can't tell you how many of those have literally come undone in my hands when I go to pull a device out...granted they are an easy service call, but scary to know that is still a n approved connection.
Top
#74337 - 01/20/07 06:33 PM Re: "back-stab" Connection Guts
Peter Offline
Member
Registered: 06/08/04
Posts: 92
Loc: San Diego
I have taken apart two and have even made drawings of them. Unfortunately, they are in TurboCad format.
Both are made of brass and are marvels of stamping engineering.
One, probably the cheaper one, has a hole slightly smaller than the wire diameter punched in it. There are two parallel slots about 1/2" long running from the top and bottom of the hole. This creates a spring which holds the wire in place. The contact area is a bit less than the circumferance of the hole times the thickness of the brass.

The other is bent in such a way to form a right angle; imagine a piece of angle iron. The wire fits into the crotch of the angle and another bit of the brass is formed into a little spring that forces the wire into the crotch. I think this is a better contact and seems to be similar to the method used in "WAGO" connectors.
~Peter
Top
#74338 - 01/20/07 07:39 PM Re: "back-stab" Connection Guts
Theelectrikid Offline
Member
Registered: 04/30/04
Posts: 810
Loc: Levittown, PA
I'll try to get a pic tomorrow when I hopefully rip out some old Slater and Leviton Recepts from the old trailer.

Ian A.
_________________________
Is there anyone on board who knows how to fly a plane?
Top
#74339 - 01/23/07 08:23 PM Re: "back-stab" Connection Guts
brianl703 Offline
Member
Registered: 05/16/05
Posts: 166
Loc: Manassas, VA
Yes, in fact, I find that the quickest way to disconnect backstab connections is to simply crush the outlet or switch with a pair of vise-grips or channelocks and then pull the wires out of the metal clips. There isn't much contact area on those. It's also scary how easy it is to crush an outlet or switch..it's much quicker than futzing around with a screwdriver to release the backstab connections.
Top
#74340 - 01/23/07 08:27 PM Re: "back-stab" Connection Guts
brianl703 Offline
Member
Registered: 05/16/05
Posts: 166
Loc: Manassas, VA
While I'm on the subject, I changed a circuit in my house (the GFCI circuit that runs into all the bathrooms and the garage) from backstab connections to pigtailed connections.

Prior to doing that, I measured the voltage drop across the circuit with a hairdryer plugged into the last outlet on the chain on high.

After I was done, I measured it again with the hairdryer on high. The voltage was about 2-3 volts higher.
Top
#74341 - 01/24/07 06:31 PM Re: "back-stab" Connection Guts
SteveFehr Offline
Member
Registered: 03/19/05
Posts: 1195
Loc: Chesapeake, VA
The infamous back-stab revealed! This is (was) a Leviton 15A 120V light-duty light switch.



Honestly, there's a surprising amount of contact area in there- there is a dimple sized for #14, and a large spring to hold it in place. The wire would have to be as straight as possible, though, or else it might only contact at 1 or 2 points instead of along the length. But installed properly, 3/8" of the wire will have contact along about 180° of circumference.

Edit: it's stamped MADE IN USA, btw

[This message has been edited by SteveFehr (edited 01-24-2007).]
Top
#74342 - 01/24/07 06:44 PM Re: "back-stab" Connection Guts
Theelectrikid Offline
Member
Registered: 04/30/04
Posts: 810
Loc: Levittown, PA
I have five pictures of a Slater Spec Grade (circa 1973) that was fully stabbed, disassembled. They start here:
http://s29.photobucket.com/albums/c266/M...nt=100_4093.jpg

I'll have to hit one with a hammer and see if I get different results.

Ian A.
_________________________
Is there anyone on board who knows how to fly a plane?
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 48 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals