#74128 - 01/13/07 07:55 AM Arc Fault
Sparks30 Offline
Member
Registered: 03/23/02
Posts: 125
Loc: Connecticut.usa
I know it been a while since I logged in, but I browse almost every night. I would like some input on a question that came up at the supply house. They are telling me the local inspector it requiring us to install 14-2-2 romex for the bedrooms. Now I have installed many Arc fault with regular 14-2 romex. Has anyone else hear of this. The 14-2-2 has two nuetrals going to it. One on the breaker and the other to the bar. Thanks
Top
Work Gear for Electricians and the Trades
#74129 - 01/13/07 08:21 AM Re: Arc Fault
Active 1 Offline
Member
Registered: 02/22/03
Posts: 687
Loc: Grayslake IL, USA
The only person that has the corect answer is the inspector or you could try and ask for the amendments/electrical code. Many places here have their building code online.

We don't use Romex here but the first thing I thought of was what if you only had a 1 BR home. Or a 2 BR you wanted to put on 1 circuit. What if the 2 BR home had the BR's on different floors or sids of the house.

My guess is just another code mith. Probibly came about by an apprentace saying why do we need to use this stuff and an owner not wanting to explain just saying bucause it's code now.
Top
#74130 - 01/13/07 08:48 AM Re: Arc Fault
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9036
Loc: Estero,Fl,usa
What would you do with the second neutral?
You need two current carrying conductors with balanced current on each. Any connection to another neutral would trip the breaker.
_________________________
Greg Fretwell
Top
#74131 - 01/13/07 08:57 AM Re: Arc Fault
e57 Offline
Member
Registered: 05/27/03
Posts: 2876
Loc: S.F.,CA USA
Considering that you are getting this information 3rd hand at the supply house counter, I would pay little head to it.

Active 1's advice about checking the local codes is a wise idea. Although there in no physical difference electricaly speaking in having 2 circuits in either (2) 12/2 cables, or a single 12/2/2 cable, there may be some other factor. For instance, localy I am required to have all conductors identified by the phase they are on, and not 'technically' the way the local code is written to phase tape them for identification, they need to have the color in the pigment of the insulation. So that means I would either have to get red/white conductor romex, or use 12/2/2. (Or 14/2/2 depending on the circuit.) FYI CH makes a 3-wire AFCI breaker....

Quote:
One on the breaker and the other to the bar.

I have no idea what purpose that would serve or why it would need to be done.... Sounds BOGUS......
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason
Top
#74132 - 01/13/07 11:56 AM Re: Arc Fault
Roger Offline
Member
Registered: 05/18/02
Posts: 1716
Loc: N.C.
Sounds to me as though the guys at the supply house get a commission on their sales.

Roger
Top
#74133 - 01/14/07 06:57 AM Re: Arc Fault
Sparks30 Offline
Member
Registered: 03/23/02
Posts: 125
Loc: Connecticut.usa
I'll check with the inspector on Monday. Just wondering what everyone else uses or has heard of this. Thanks
Top
#74134 - 01/14/07 07:52 AM Re: Arc Fault
dilydalyer Offline
Member
Registered: 01/08/07
Posts: 59
Loc: tennessee
Never heard of any of this throughout the Florida romex panhandle...
Top
#74135 - 01/14/07 10:14 AM Re: Arc Fault
RobbieD Offline
Member
Registered: 02/23/03
Posts: 231
Loc: Canada
This is from-

[url= http://www.mikeholt.com/mojonewsarchive/AFCI-HTML/HTML/AFCI_Update~20030320.htm] http://www.mikeholt.com/mojonewsarchive/AFCI-HTML/HTML/AFCI_Update~20030320.htm[/url]


12-2-2 NM “Romex” was introduced to allow home runs for two AFCI circuits, as an AFCI can not have a shared neutral (due to ground fault protection). However, at least one manufacturer (Cutler Hammer) offers a 2-pole AFCI for home runs. Standard 12-2-1 NM “Romex” can be used. The 2-pole AFCIs are available with/without common trip for overcurrent and overload conditions; the trip is always common for an arcing or ground fault.
Top
#74136 - 01/14/07 10:27 AM Re: Arc Fault
Roger Offline
Member
Registered: 05/18/02
Posts: 1716
Loc: N.C.
Robbie, that makes sense.

Roger
Top
#74137 - 01/14/07 05:11 PM Re: Arc Fault
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9036
Loc: Estero,Fl,usa
All this to save a ground wire?
I can't imagine you are saving that much money.
_________________________
Greg Fretwell
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 04/03/02
Posts: 6775
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 14 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals