#73975 - 01/07/07 09:11 AM 5 KVA TX
Cinner Offline
Member
Registered: 12/01/04
Posts: 78
Loc: Kelowna, B.C., Canada
We mounted a 5 KVA transformer on top of a control panel at work. We used a 2" chase nipple to bring in the primary and secondary into the panel(600v and 120v). The line and load are in the panel. Therefore we had to bring the line 600v into the chase nipple and then the load 120 back out. Is it o.k. to bring the 2 different voltages 600 and 120 through the SAME chase nipple aproximately 2 " long?
Top
Work Gear for Electricians and the Trades
#73976 - 01/07/07 09:16 AM Re: 5 KVA TX
SteveFehr Offline
Member
Registered: 03/19/05
Posts: 1195
Loc: Chesapeake, VA
If the insulation on all wires is rated for 600V, then yes, it's OK to have 120V and 600V in the same raceway.

Does derating apply to a 2" nipple, though?

[This message has been edited by SteveFehr (edited 01-07-2007).]
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6778
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 57 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals