The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Safety at heights?
by HotLine1
Yesterday at 08:51 PM
International Wire Colour Codes
by Texas_Ranger
Yesterday at 03:29 PM
Looking for older post
by Texas_Ranger
Yesterday at 03:22 PM
Last time to chat here
by Trumpy
01/20/17 11:41 PM
Unsafe Situations
by Trumpy
01/20/17 09:46 PM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
Admin 35
HotLine1 20
Ruben Rocha 17
gfretwell 16
Trumpy 15
Who's Online
0 registered (), 74 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#73975 - 01/07/07 09:11 AM 5 KVA TX
Cinner Offline
Member

Registered: 12/01/04
Posts: 77
Loc: Kelowna, B.C., Canada
We mounted a 5 KVA transformer on top of a control panel at work. We used a 2" chase nipple to bring in the primary and secondary into the panel(600v and 120v). The line and load are in the panel. Therefore we had to bring the line 600v into the chase nipple and then the load 120 back out. Is it o.k. to bring the 2 different voltages 600 and 120 through the SAME chase nipple aproximately 2 " long?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#73976 - 01/07/07 09:16 AM Re: 5 KVA TX
SteveFehr Offline
Member

Registered: 03/19/05
Posts: 1192
Loc: Chesapeake, VA
If the insulation on all wires is rated for 600V, then yes, it's OK to have 120V and 600V in the same raceway.

Does derating apply to a 2" nipple, though?

[This message has been edited by SteveFehr (edited 01-07-2007).]