The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Yesterday at 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
1 registered (HotLine1), 214 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#73790 - 01/02/07 07:26 PM First Time I ever saw this!
BigB Offline
Member

Registered: 03/31/04
Posts: 727
Loc: Tucson, AZ USA
Went to look at a 200 amp upgrade job today and found two 2 wire (with ground) Romexes being used as multiwire circuits. The black and the white were the two lines and the bare was the neutral. Looked like it was done at construction, 30 year old house out in the sticks.

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#73791 - 01/02/07 07:37 PM Re: First Time I ever saw this!
ShockMe77 Offline
Member

Registered: 06/11/05
Posts: 823
Loc: Rahway, New Jersey
I've definitely never seen that before!

Top
#73792 - 01/02/07 08:19 PM Re: First Time I ever saw this!
mxslick Offline
Member

Registered: 10/24/04
Posts: 785
Loc: Atomic City, ID USA
Another reason why I hate multi wire circuits!!

O.k., brace for a "blast" from iwire!!
_________________________
Stupid should be painful.

Top
#73793 - 01/02/07 08:21 PM Re: First Time I ever saw this!
Lostazhell Offline
Member

Registered: 02/21/04
Posts: 1248
Loc: Bakersfield, CA (Originally Or...
Not that I ever think that was code, what were the loads they were feeding?

Top
#73794 - 01/02/07 10:29 PM Re: First Time I ever saw this!
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
This sort of thing happens when a guy screws up the rough and finds it at trim. Instead of admitting it and eating the backcharge for drywall and paint they cheat.
My wife caught some 3 ways wired the same way, using the bare as a current carrying conductor.
_________________________
Greg Fretwell

Top
#73795 - 01/03/07 01:50 AM Re: First Time I ever saw this!
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
 Quote:
Another reason why I hate multi wire circuits!!
O.k., brace for a "blast" from iwire!!


I don't like any mis-wired circuit.

Really wondering how you would wire a electric dryer or range?

Those are both multiwire branch circuits.



[This message has been edited by iwire (edited 01-03-2007).]
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#73796 - 01/03/07 01:52 AM Re: First Time I ever saw this!
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
It would not surprise me if some of the projectors you use require multi wire branch circuits.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#73797 - 01/03/07 05:39 AM Re: First Time I ever saw this!
TwinCitySparky Offline
Member

Registered: 03/23/06
Posts: 52
Loc: Minnesota
An electrician who is uncomfortable running MWC's -- Kind of like a doctor who is afraid of using his stethescope. It must be very un-nerving dealing with that great big service entrance MWC while doing a panel changout. Probly not wiring many large homes either. I'd like to see some of the home runs in said installations, and the bid...

Top
#73798 - 01/03/07 06:37 AM Re: First Time I ever saw this!
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
When I was young, wet behind the ears, and had just moved out "on my own," I rented a room in a house that housed several such as I.

My 'introduction' to the trade came when a very upset man appeared one day, looking for one of the other residents. He had hired the guy to do some electric work in his new home, he said, and the guy did something wrong, that 'blew up' hs TV set.

Later, in the course of my work, I was introduced to properly trained, real electricians. The bits and pieces I told of the story made no sense to them.

With hindsight, of course it was not something the 'real' guys had ever dealt with; they had been taught right, and had not done what this self-taught self-appointed "electrician" had done - they had never left an open (or loose) neutral.

Much as I value saving money myself, I draw the line at 'cheating.' I don't hire the local 'aw shucks' guy to do my brakes; nor do I try to do my own haircuts! So many of the problems we encounter (and the pictures we post) are the result of someone trying to 'beat the system.'

It is one thing, in dire circumstances, to try to "McGyver" something; quite another to make such "self-reliance" one of your lifes' basic principles.

Top
#73799 - 01/03/07 06:56 AM Re: First Time I ever saw this!
denversparky Offline
Member

Registered: 02/02/05
Posts: 17
Loc: colorado
Well said Reno

Top