#73526 - 12/27/06 06:44 PM Damp or wet location lay in fixtures?
kyelectric Offline
Member
Registered: 08/30/05
Posts: 64
I am installing 2x4 lay in flourescent fixtures in a large company bathroom with a changing area and large walk in shower. The hanging ceiling installer went right into the shower area with the hanging ceiling and left me holes to install the 2x4 lay in fixtures there too. Is it ok to install these in the shower area or do they have to be a specific light fixture approved for a wet location?
Top
Work Gear for Electricians and the Trades
#73527 - 12/27/06 07:19 PM Re: Damp or wet location lay in fixtures?
power one Offline
Junior Member
Registered: 08/28/02
Posts: 4
Loc: Corona, Ca. 92882
I believe you need fixtures that are vapor proof. They have a weather tight seal around the lens.
Top
#73528 - 12/27/06 08:53 PM Re: Damp or wet location lay in fixtures?
Obsaleet Offline
Member
Registered: 04/05/03
Posts: 362
Loc: Pa
I used wet location listed flourescents 2x4 lay in a bathroom in a girls school. They look just like lay ins but have foam gaskets. They were a stock item at my 1 supplier.

Ob
_________________________
Choose your customers, don't let them choose you.
Top
#73529 - 12/27/06 09:12 PM Re: Damp or wet location lay in fixtures?
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9038
Loc: Estero,Fl,usa
How high are they? If it is over 8' I think they are out of the zone. It is still not a bad idea to find something damp rated tho, just for the next guy who has to fix them when they corrode. I do believe is is a design issue above 8', not a code issue.
_________________________
Greg Fretwell
Top

Member Spotlight
Member Since: 10/07/00
Posts: 3417
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 54 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals