The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Safety at heights?
by gfretwell
Today at 02:19 AM
Looking for older post
by Trumpy
Today at 01:04 AM
Last time to chat here
by Trumpy
Yesterday at 11:41 PM
Unsafe Situations
by Trumpy
Yesterday at 09:46 PM
Webmaster > Admin
by Trumpy
Yesterday at 08:29 PM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
Admin 35
HotLine1 20
Trumpy 19
Ruben Rocha 17
gfretwell 16
Who's Online
1 registered (Ruben Rocha), 157 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#7347 - 01/31/02 06:12 PM sizing service entrance cable
rodney2 Offline
Junior Member

Registered: 01/31/02
Posts: 2
Loc: Indianapolis,In.
600 A 208/120 what size and could I pair

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#7348 - 02/01/02 07:09 AM Re: sizing service entrance cable
WARREN1 Offline
Member

Registered: 05/09/01
Posts: 184
Loc: Greenville, SC, USA
I assume this to be some commercial or light industrial service and that the calculations per Art 220 are in proper order. Then the lookup is in Art 310, Table 310-**, depending your application. My first guess is Table 310-16. Look down the 75 degree colume to 310Amps which is for a 350 kcMil copper cable, Type (as listed at the top of the column). Paralleling this cable brings you to 620 amps. Make temperature corrections, if required. You may use the 90 degree rating to accomplish this. Remember parallel cables must be cut to the exact same length.
YOu can use the same size neutral, or size it based on calculation in Art. 220-22.
The grounding electrode conductor is based on Table 250-66, equivalent area for parallel conductors, which would be a 2/0 copper conductor.
Hope this helps.

Top
#7349 - 02/01/02 09:27 AM Re: sizing service entrance cable
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
Note that if the grounded conductor is sized per the Article 220 calculations that systems with very small calculated grounded conductor loads will have to comply with 250-24(b)(1) for the grounded conductor size.
Don(resqcapt19)
_________________________
Don(resqcapt19)

Top


ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals