The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by ghost307
Today at 04:10 PM
International Wire Colour Codes
by Tjia1981
Today at 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 12
HotLine1 7
renosteinke 6
ghost307 6
Potseal 4
Who's Online
0 registered (), 255 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#73255 - 12/20/06 05:05 PM restoring plated bus bar
rgh Offline
Junior Member

Registered: 02/26/05
Posts: 1
Loc: Newmarket, Ontario, Canada
I just returned from a residential call where a bolted connection on the aluminum bus had over time, become loose and has over heated. The plating has dulled and the bolt holding the connection of two piece bus has that terrible squeek to it when it is either tightened or loosened. It is an out of production panel, and suspect I will not find replacement parts. Is there an acceptable way of cleaning, polishing and retreating the bus to put it back in service ?

Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#73256 - 12/20/06 05:09 PM Re: restoring plated bus bar
Lostazhell Offline

Registered: 02/21/04
Posts: 1248
Loc: Bakersfield, CA (Originally Or...
you can always have a new piece fabricated... but I have to ask.... Why not just install a new service?

#73257 - 12/20/06 06:10 PM Re: restoring plated bus bar
LK Offline


Registered: 01/21/03
Posts: 1721
Loc: New Jersey
"a bolted connection on the aluminum bus had over time, become loose and has over heated."

I would replace the loadcenter, not worth the the liability risk.

#73258 - 12/20/06 08:08 PM Re: restoring plated bus bar
BigB Offline

Registered: 03/31/04
Posts: 725
Loc: Tucson, AZ USA
Even if you can clean it up and re tighten it, it will fail again. I am pretty sure the aluminum is coated with tin, which is now gone. I have patched them up enough to last a few days till we could change it out. But as the others have said, it needs to be changed out ASAP.

#73259 - 12/20/06 08:17 PM Re: restoring plated bus bar
EV607797 Offline

Registered: 10/25/06
Posts: 756
Loc: Fredericksburg, VA, USA
If you had a custom replacement made, you would be messing with the panel's UL listing by installing non-factory parts. If any metal has been heated to the point that it has been discolored, it can't be trusted anymore, electrically or physically. It must be replaced.

There are lots of companies selling used breakers and panels on the Internet; I would go there via Google to get started. The liability associated with this is way too high to risk replacement with custom-made replacement parts.

By the way, I don't know what brand the panel is that you mentioned, but there is an Eaton (Cutler-Hammer and Westinghouse) facility in Sumter, SC that handles obsolete/out of production products for these brands.

[This message has been edited by EV607797 (edited 12-20-2006).]

"But the guy at Home Depot said it would work."

#73260 - 12/23/06 03:56 AM Re: restoring plated bus bar
iwire Offline

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
New Panel time
Bob Badger
Construction & Maintenance Electrician