The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Would ELV branch circuits be a good idea?
by LongRunner
Today at 07:42 AM
100% breakers?
by Texas_Ranger
Today at 06:13 AM
Forum Software Upgrade coming soon...
by Trumpy
01/14/17 07:11 PM
Faricating Guards out if Lexan?
by Trumpy
01/14/17 07:09 PM
Dangerous DIY Advice
by Potseal
01/12/17 09:52 AM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
HotLine1 16
gfretwell 11
sparkyinak 10
ghost307 10
Webmaster 8
Who's Online
1 registered (brsele), 280 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#73046 - 12/15/06 02:36 PM Delayed tripping RCD?
Alan Belson Offline
Member

Registered: 03/23/05
Posts: 1801
Loc: Mayenne N. France
Went to visit a friend today. He has an oil filled electric towel-rail in the bathroom, 700W @ 230v. It's practically brand new and worked fine when [ professionally ] installed, but he's been away in England for several weeks. The whole house has been professionally rewired right back to new consumer unit / panels. When plugged in it runs for 30 seconds, then trips the 30ma RCD unit. I put a meter on the plug [ cord-cap ] terminals and got a reading of about 9000 ohms hot to ground, ie a leakage of about 20ma with the unit cold. I told him to get the electrician back in to fix the problem as he has a serious fault, but why does it trip out after 30 seconds?

Alan

[This message has been edited by Alan Belson (edited 12-15-2006).]
_________________________
Wood work but can't!

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#73047 - 12/15/06 05:09 PM Re: Delayed tripping RCD?
Trumpy Offline


Member

Registered: 07/05/02
Posts: 8548
Loc: SI,New Zealand
Thermal expansion of some kind in the element inside the oil chamber possibly Alan?.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top
#73048 - 12/15/06 07:11 PM Re: Delayed tripping RCD?
JoeTestingEngr Offline
Member

Registered: 11/04/05
Posts: 786
Loc: Chicago, Il.
Could there possibly be enough inductive reactance to reduce the AC current to borderline? I really question the mfg. tolerances on GFCIs. I faulted hot to ground through my Fluke and a variable resistor on a GFCI at work. It didn't trip until about 9mA, which was more than I expected. I had tested one this way in response to a thread here where someone had suggested using a Wiggy to test a GFCI. I seem to remember the Wiggy flowing a current several times that considered lethal.
Joe

Top
#73049 - 12/16/06 06:35 AM Re: Delayed tripping RCD?
Kenbo Offline
Member

Registered: 04/07/06
Posts: 234
Loc: Scotland
Alan

Have a quick look at this link see if it helps

IEE-Understanding RCDs

Kenny
_________________________
der Gro├čvater

Top
#73050 - 12/16/06 10:01 AM Re: Delayed tripping RCD?
pauluk Offline
Member

Registered: 08/11/01
Posts: 7693
Loc: Norfolk, England
Heating elements can often develop a fault in which they short out to the grounded casing as they heat up.

I'd disconnect the element entirely from the thermostat/timer/switching and megger it, although if you've already read 9 kohms on a low-voltage DC test that probably confirms it anyway.