#73046 - 12/15/06 02:36 PM Delayed tripping RCD?
Alan Belson Offline
Member
Registered: 03/23/05
Posts: 1803
Loc: Mayenne N. France
Went to visit a friend today. He has an oil filled electric towel-rail in the bathroom, 700W @ 230v. It's practically brand new and worked fine when [ professionally ] installed, but he's been away in England for several weeks. The whole house has been professionally rewired right back to new consumer unit / panels. When plugged in it runs for 30 seconds, then trips the 30ma RCD unit. I put a meter on the plug [ cord-cap ] terminals and got a reading of about 9000 ohms hot to ground, ie a leakage of about 20ma with the unit cold. I told him to get the electrician back in to fix the problem as he has a serious fault, but why does it trip out after 30 seconds?

Alan

[This message has been edited by Alan Belson (edited 12-15-2006).]
_________________________
Wood work but can't!
Top
Work Gear for Electricians and the Trades
#73047 - 12/15/06 05:09 PM Re: Delayed tripping RCD?
Trumpy Offline


Member
Registered: 07/05/02
Posts: 8211
Loc: SI,New Zealand
Thermal expansion of some kind in the element inside the oil chamber possibly Alan?.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin
Top
#73048 - 12/15/06 07:11 PM Re: Delayed tripping RCD?
JoeTestingEngr Offline
Member
Registered: 11/04/05
Posts: 781
Loc: Chicago, Il.
Could there possibly be enough inductive reactance to reduce the AC current to borderline? I really question the mfg. tolerances on GFCIs. I faulted hot to ground through my Fluke and a variable resistor on a GFCI at work. It didn't trip until about 9mA, which was more than I expected. I had tested one this way in response to a thread here where someone had suggested using a Wiggy to test a GFCI. I seem to remember the Wiggy flowing a current several times that considered lethal.
Joe
Top
#73049 - 12/16/06 06:35 AM Re: Delayed tripping RCD?
Kenbo Offline
Member
Registered: 04/07/06
Posts: 233
Loc: Scotland
Alan

Have a quick look at this link see if it helps

IEE-Understanding RCDs

Kenny
_________________________
der Gro├čvater
Top
#73050 - 12/16/06 10:01 AM Re: Delayed tripping RCD?
pauluk Offline
Member
Registered: 08/11/01
Posts: 7520
Loc: Norfolk, England
Heating elements can often develop a fault in which they short out to the grounded casing as they heat up.

I'd disconnect the element entirely from the thermostat/timer/switching and megger it, although if you've already read 9 kohms on a low-voltage DC test that probably confirms it anyway.
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (sparkyinak), 57 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals