The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/24/16 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm▓ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
ghost307 7
HotLine1 7
renosteinke 6
Potseal 4
Who's Online
2 registered (HotLine1, gfretwell), 304 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#73046 - 12/15/06 02:36 PM Delayed tripping RCD?
Alan Belson Offline

Registered: 03/23/05
Posts: 1801
Loc: Mayenne N. France
Went to visit a friend today. He has an oil filled electric towel-rail in the bathroom, 700W @ 230v. It's practically brand new and worked fine when [ professionally ] installed, but he's been away in England for several weeks. The whole house has been professionally rewired right back to new consumer unit / panels. When plugged in it runs for 30 seconds, then trips the 30ma RCD unit. I put a meter on the plug [ cord-cap ] terminals and got a reading of about 9000 ohms hot to ground, ie a leakage of about 20ma with the unit cold. I told him to get the electrician back in to fix the problem as he has a serious fault, but why does it trip out after 30 seconds?


[This message has been edited by Alan Belson (edited 12-15-2006).]
Wood work but can't!

Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#73047 - 12/15/06 05:09 PM Re: Delayed tripping RCD?
Trumpy Offline


Registered: 07/05/02
Posts: 8532
Loc: SI,New Zealand
Thermal expansion of some kind in the element inside the oil chamber possibly Alan?.
Let's face it, these days if you're not young, you're old - Red Green grin

#73048 - 12/15/06 07:11 PM Re: Delayed tripping RCD?
JoeTestingEngr Offline

Registered: 11/04/05
Posts: 786
Loc: Chicago, Il.
Could there possibly be enough inductive reactance to reduce the AC current to borderline? I really question the mfg. tolerances on GFCIs. I faulted hot to ground through my Fluke and a variable resistor on a GFCI at work. It didn't trip until about 9mA, which was more than I expected. I had tested one this way in response to a thread here where someone had suggested using a Wiggy to test a GFCI. I seem to remember the Wiggy flowing a current several times that considered lethal.

#73049 - 12/16/06 06:35 AM Re: Delayed tripping RCD?
Kenbo Offline

Registered: 04/07/06
Posts: 234
Loc: Scotland

Have a quick look at this link see if it helps

IEE-Understanding RCDs

der Gro├čvater

#73050 - 12/16/06 10:01 AM Re: Delayed tripping RCD?
pauluk Offline

Registered: 08/11/01
Posts: 7693
Loc: Norfolk, England
Heating elements can often develop a fault in which they short out to the grounded casing as they heat up.

I'd disconnect the element entirely from the thermostat/timer/switching and megger it, although if you've already read 9 kohms on a low-voltage DC test that probably confirms it anyway.