need to know what size groung conductor to use for the main ground to the water pipe for a 1600 amp service with 4 sets of 600 mcm cables to the utility transformer.
Top
Work Gear for Electricians and the Trades
#72995 - 12/14/06 06:24 PM Re: ground size
Luketrician Offline
Member
Registered: 07/08/06
Posts: 272
Loc: Sale Creek, TN USA
With the information given, table 250.122 shows 4/0 if the egc is copper, or 350 if it's al/cu. 250.122 (F) talks about conductors in parallel also. This should get you started.
_________________________
Luke Clarke
Electrical Planner for TVA.

Top
#72996 - 12/14/06 07:58 PM Re: ground size
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
You use 250.66, not 250.122
I read it as the max required will be 3/0 copper or 250 MCM al.
_________________________
Greg Fretwell
Top
#72997 - 12/14/06 08:23 PM Re: ground size
Luketrician Offline
Member
Registered: 07/08/06
Posts: 272
Loc: Sale Creek, TN USA
Thanks, and apologies for the mix-up, 250.122 is for grounding raceway's and equipment. Seen that first part, where it says minimum size egc, and the rest is history.
_________________________
Luke Clarke
Electrical Planner for TVA.

Top
#72998 - 12/16/06 06:10 PM Re: ground size
Yoopersup Offline
Member
Registered: 03/04/03
Posts: 822
Loc: Michigan
If under the Chicago code its 18-27-250.66 page 93
copper (300) in a 1 1/4 inch conduit or tubing.
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 45 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals