The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
Trumpy 8
sparkyinak 7
Who's Online
1 registered (sparkyinak), 220 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#72964 - 12/12/06 07:54 PM line side of disconnect
sudsy4 Offline
Member

Registered: 04/24/02
Posts: 32
Loc: Elizabeth,PA USA
Is there a requirement for line side conductors to be terminated on the top of a disconnect, or was that just a known way to do it. Been seeing alot of factory wired equipment pre-wired with the line conductors expected to terminate at the bottom of the disconnect device (breaker).
For 35 years, this was always unexceptable to me...line top, load bottom.
_________________________
Bill

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#72965 - 12/12/06 09:01 PM Re: line side of disconnect
Rich Thomas Offline
Member

Registered: 03/09/05
Posts: 48
Loc: Seattle, Washington, USA
That's a good question.

I also thought line was on top. I thought line had to be on top so the arc squelch mechanism operated correctly when the breaker opens.

Top
#72966 - 12/12/06 11:22 PM Re: line side of disconnect
e57 Offline
Member

Registered: 05/27/03
Posts: 2837
Loc: S.F.,CA USA
In the trade for about 1/2 of that 35, and I too remember it the same way, but have noticed that it is no longer the case. I'm sure it was a requirement at some point, but can't tell you when it was removed - But I think "Line" was stamped at the top for everything for quite some time after that. "line on top" - is something that I was always told....

Or, maybe the last vestages of any wording that may have implied it are in 404.6(A-C)

"Single-throw knife switches shall be placed so that gravity will not tend to close them." And, by design... it ended up that way - 'Line on top'.
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason

Top
#72967 - 12/13/06 01:42 AM Re: line side of disconnect
jraef Offline
Member

Registered: 07/21/04
Posts: 91
Loc: San francisco, CA, USA
I'm not 100% sure, but I believe the issue is, you are required to connect in the manner proscribed by the device manufacturer, and they almost all say Line on top, Load on bottom. If you have to do it differently for some reason, you have to get special labels indicating the change so that some future electrician would not make a careless mistake by assuming the convention. I got that info from an inspector on a job where I had to back-feed a main circuit breaker.
_________________________
JRaef

Top
#72968 - 12/13/06 01:56 AM Re: line side of disconnect
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Not many single throw switching devices are marked line and load anymore.

Fused disconnects have to de-energize the fuses, that eliminates any options with those.

Most breakers can be used any direction,

 Quote:
I got that info from an inspector on a job where I had to back-feed a main circuit breaker.


I agree it is a good idea bit the inspector was asking for something that is not required by the NEC

 Quote:
Or, maybe the last vestages of any wording that may have implied it are in 404.6(A-C)

"Single-throw knife switches shall be placed so that gravity will not tend to close them." And, by design... it ended up that way - 'Line on top'.


Once you get to double throw (a manual ATS for example) that goes out the window.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#72969 - 12/13/06 09:19 AM Re: line side of disconnect
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
The only limiting rule is the way the handle operates.
_________________________
Greg Fretwell

Top
#72970 - 12/13/06 09:23 AM Re: line side of disconnect
Helectric Offline
Member

Registered: 01/07/05
Posts: 91
Loc: Brandon, SD
I think that 404.6 is about it for code regarding this.

Top
#72971 - 12/13/06 07:22 PM Re: line side of disconnect
sudsy4 Offline
Member

Registered: 04/24/02
Posts: 32
Loc: Elizabeth,PA USA
Thanks for the replies