#72964 - 12/12/06 07:54 PM line side of disconnect
sudsy4 Offline
Member
Registered: 04/24/02
Posts: 32
Loc: Elizabeth,PA USA
Is there a requirement for line side conductors to be terminated on the top of a disconnect, or was that just a known way to do it. Been seeing alot of factory wired equipment pre-wired with the line conductors expected to terminate at the bottom of the disconnect device (breaker).
For 35 years, this was always unexceptable to me...line top, load bottom.
_________________________
Bill
Top
Work Gear for Electricians and the Trades
#72965 - 12/12/06 09:01 PM Re: line side of disconnect
Rich Thomas Offline
Member
Registered: 03/09/05
Posts: 48
Loc: Seattle, Washington, USA
That's a good question.

I also thought line was on top. I thought line had to be on top so the arc squelch mechanism operated correctly when the breaker opens.
Top
#72966 - 12/12/06 11:22 PM Re: line side of disconnect
e57 Offline
Member
Registered: 05/27/03
Posts: 2876
Loc: S.F.,CA USA
In the trade for about 1/2 of that 35, and I too remember it the same way, but have noticed that it is no longer the case. I'm sure it was a requirement at some point, but can't tell you when it was removed - But I think "Line" was stamped at the top for everything for quite some time after that. "line on top" - is something that I was always told....

Or, maybe the last vestages of any wording that may have implied it are in 404.6(A-C)

"Single-throw knife switches shall be placed so that gravity will not tend to close them." And, by design... it ended up that way - 'Line on top'.
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason
Top
#72967 - 12/13/06 01:42 AM Re: line side of disconnect
jraef Offline
Member
Registered: 07/21/04
Posts: 93
Loc: San francisco, CA, USA
I'm not 100% sure, but I believe the issue is, you are required to connect in the manner proscribed by the device manufacturer, and they almost all say Line on top, Load on bottom. If you have to do it differently for some reason, you have to get special labels indicating the change so that some future electrician would not make a careless mistake by assuming the convention. I got that info from an inspector on a job where I had to back-feed a main circuit breaker.
_________________________
JRaef
Top
#72968 - 12/13/06 01:56 AM Re: line side of disconnect
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
Not many single throw switching devices are marked line and load anymore.

Fused disconnects have to de-energize the fuses, that eliminates any options with those.

Most breakers can be used any direction,

Quote:
I got that info from an inspector on a job where I had to back-feed a main circuit breaker.


I agree it is a good idea bit the inspector was asking for something that is not required by the NEC

Quote:
Or, maybe the last vestages of any wording that may have implied it are in 404.6(A-C)

"Single-throw knife switches shall be placed so that gravity will not tend to close them." And, by design... it ended up that way - 'Line on top'.


Once you get to double throw (a manual ATS for example) that goes out the window.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#72969 - 12/13/06 09:19 AM Re: line side of disconnect
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
The only limiting rule is the way the handle operates.
_________________________
Greg Fretwell
Top
#72970 - 12/13/06 09:23 AM Re: line side of disconnect
Helectric Offline
Member
Registered: 01/07/05
Posts: 90
Loc: Brandon, SD
I think that 404.6 is about it for code regarding this.
Top
#72971 - 12/13/06 07:22 PM Re: line side of disconnect
sudsy4 Offline
Member
Registered: 04/24/02
Posts: 32
Loc: Elizabeth,PA USA
Thanks for the replies
_________________________
Bill
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 67 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
KrmtFrg, Stack, Scotto, Freecrowder, clee512

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals