#72947 - 12/12/06 11:40 AM Code Wiring Question
wendel Offline
Member
Registered: 08/07/04
Posts: 55
Is it a violation of the national electric code to use 14-3 wire for simple, non-3way 15 amp circuit? The original plan called for some 3 way switches that were not installed after the 3 way wiring had been done. The electrician used wire nuts to cap the red lead in every box it wasn't used.
Top
Work Gear for Electricians and the Trades
#72948 - 12/12/06 11:52 AM Re: Code Wiring Question
rabbitgun Offline
Member
Registered: 07/25/06
Posts: 23
No worries wendel. No worries at all.
Top
#72949 - 12/12/06 12:13 PM Re: Code Wiring Question
EV607797 Offline
Member
Registered: 10/25/06
Posts: 744
Loc: Fredericksburg, VA, USA
I sure wish that more people made that "mistake". It's almost as nice as having EMT to allow you to get another circuit in. I would thank them for the change in plans.

[This message has been edited by EV607797 (edited 12-12-2006).]
_________________________
---Ed---

"But the guy at Home Depot said it would work."
Top
#72950 - 12/12/06 04:06 PM Re: Code Wiring Question
ElJay Offline
Junior Member
Registered: 06/29/06
Posts: 7
Loc: Spartanburg, S.C.
I've personally seen this many times.
Top
#72951 - 12/12/06 07:33 PM Re: Code Wiring Question
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
The scary thing is how many times you find 2 wire used on a 3 way leg using the ground.
_________________________
Greg Fretwell
Top
#72952 - 12/12/06 08:51 PM Re: Code Wiring Question
Rich Thomas Offline
Member
Registered: 03/09/05
Posts: 48
Loc: Seattle, Washington, USA
Precaution. I know this is not on your subject, but, check the trip rating of the circuit breaker to make sure it's 15 Amp and not 20 Amp.

I've seen cases where the plans call for #12 AWG with a 20/1 breaker in the panelboard and #14 AWG was installed. This would be a violation of the NEC.
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 51 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals