#72864 - 12/11/06 04:31 PM Washing machine
Sparks30 Offline
Member
Registered: 03/23/02
Posts: 125
Loc: Connecticut.usa
Ran a new circuit 20 amp for washer,is there any code stating that it must be a dedicted circuit.Thanks Also how about the 220 and 120 volt wires being taped together for about half the run to a pvc pipe. Is this considered bundling.

[This message has been edited by Sparks30 (edited 12-11-2006).]
Top
Work Gear for Electricians and the Trades
#72865 - 12/11/06 04:43 PM Re: Washing machine
pauluk Offline
Member
Registered: 08/11/01
Posts: 7520
Loc: Norfolk, England
210.11(C)(2):

Quote:
In addition to the number of branch circuits required by other parts of this section, at least one additional 20-ampere branch circuit shall be provided to supply the laundry receptacle outlet(s) required by 210.52(F). This circuit shall have no other outlets.
Top
#72866 - 12/11/06 04:47 PM Re: Washing machine
Sparks30 Offline
Member
Registered: 03/23/02
Posts: 125
Loc: Connecticut.usa
Thanks I missed that article. I did not do this work, another company did and the inspector pasted it. I am friends with the head inspector, just looking want somebacking when I talk to him about his help.
Top
#72867 - 12/11/06 05:29 PM Re: Washing machine
HLCbuild Offline
Member
Registered: 12/05/04
Posts: 209
Loc: Herndon,Va USA
I read 210-11(C)2 as requiring a dedicated circuit for the laundry outlet(s) but 210-52(F) says you can have more than one outlet on this circuit. It just can't leave the laundry area.
Top
#72868 - 12/11/06 06:08 PM Re: Washing machine
mister h Offline
Member
Registered: 05/26/06
Posts: 20
Loc: erie, pa. usa
If you have a laundry sink within six feet of the edge the dedicated laundry circuit(210.11(C)(2) has to be GFCI protected. 210.8(7).

Ken
_________________________
ken
Top
#72869 - 12/11/06 06:34 PM Re: Washing machine
Obsaleet Offline
Member
Registered: 04/05/03
Posts: 362
Loc: Pa
gfci for the washer only if it is a duplex. It should be a single receptacle. Then it is a fixed appliance? And they won't have to call me to reset GFCI when it tripps

Ob
_________________________
Choose your customers, don't let them choose you.
Top
#72870 - 12/11/06 06:41 PM Re: Washing machine
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
There is no relief for a single appliance if the receptacle is within 6' of the sink.

Taped together for more than 2' is "bundled" but if you are using a 90c conductor you are still within the ampacity when you derate to 80%.
_________________________
Greg Fretwell
Top
#72871 - 12/11/06 07:24 PM Re: Washing machine
Sparks30 Offline
Member
Registered: 03/23/02
Posts: 125
Loc: Connecticut.usa
There is no sink, just a washer and dryer. They want to use the duplex that is on the washer for a mini fridge and exhaust fan for the bathroom in the next room.

The wires that are taped together are #10-3 romex and #12-2 romex.
Top
#72872 - 12/11/06 08:25 PM Re: Washing machine
EV607797 Offline
Member
Registered: 10/25/06
Posts: 744
Loc: Fredericksburg, VA, USA
No dice on the exhaust fan and fridge in the next room. The circuit can't leave the laundry area or room for anything.
_________________________
---Ed---

"But the guy at Home Depot said it would work."
Top
#72873 - 12/12/06 03:36 AM Re: Washing machine
Sparks30 Offline
Member
Registered: 03/23/02
Posts: 125
Loc: Connecticut.usa
The fridge is n the same room.
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 48 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals