The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
International Wire Colour Codes
by Texas_Ranger
Today at 08:24 AM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
230 or 345 kV transmission lines?
by annemarie1
10/12/16 01:23 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
HotLine1 6
renosteinke 6
ghost307 5
Potseal 4
Who's Online
1 registered (hyetal), 201 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#72843 - 12/11/06 03:03 PM 200a sub lugs
harlie_7 Offline
Junior Member

Registered: 12/11/06
Posts: 1
I have a 200A panal in my house and would like to put a 200A sub in my barn. I know seimans dont make a 200A 2pole breaker. Is there a lug kit i can put in this panal to feed the sub? Any other options?

Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#72844 - 12/11/06 03:30 PM Re: 200a sub lugs
Roger Offline

Registered: 05/18/02
Posts: 1779
Loc: N.C.
Harlie, contact a local Electrician, they will be able to help you.


#72845 - 12/12/06 04:42 PM Re: 200a sub lugs
circuit man Offline

Registered: 11/05/01
Posts: 287
Loc: saluda,s.c.
harlie, why not put a seperate meter on the barn? copper is pretty expensive for a 200 amp feed,unless it's real short. but as roger said please contact an electrician

#72846 - 12/12/06 07:00 PM Re: 200a sub lugs
ShockMe77 Offline

Registered: 06/11/05
Posts: 823
Loc: Rahway, New Jersey
What kinds of loads will there be in the barn?

#72847 - 12/12/06 07:26 PM Re: 200a sub lugs
electure Offline


Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
I can't think of a reason that you would want to put in a 200A subpanel fed from a 200A panel.
If your load in the barn is that great, chances are you would need to upgrade the service at the house.
I don't know if it's an alternative, but will the PoCo give you a separate service at the barn?

#72848 - 12/12/06 09:05 PM Re: 200a sub lugs
SolarPowered Offline

Registered: 07/05/04
Posts: 615
Loc: Palo Alto, CA, USA
I'm guessing that Harlie has, or has his eye on, a "200A panel", and figures that he needs to supply it with a 200A supply.

Harlie, that's not necessary. Your supply needs to be sized according to the load calcs in the Code, which will almost certainly be less than 200A. It is very likely you can feed your 200A panel with a 50-100A feeder.

[This message has been edited by SolarPowered (edited 12-13-2006).]

#72849 - 12/12/06 11:32 PM Re: 200a sub lugs
e57 Offline

Registered: 05/27/03
Posts: 2837
Loc: S.F.,CA USA
"seimans dont make a 200A 2pole breaker."

They don't?!?

Edit due to pic's being so big you could see the finger-prints of the photographer.....

[This message has been edited by e57 (edited 12-13-2006).]
Mark Heller
"Well - I oughta....." -Jackie Gleason

#72850 - 12/13/06 03:47 AM Re: 200a sub lugs
Eddy Current Offline

Registered: 09/26/06
Posts: 112
Loc: Ontario,Canada
All panels have a "per stabb" rating on the inside of the cover. A 200a panel usually has a max of about 70a per stabb. You can't run a 200a circuit from a 200a pqnel. Check the "per stabb" rating on the panel.

#72851 - 12/13/06 04:43 AM Re: 200a sub lugs
watthead Offline

Registered: 10/13/01
Posts: 182
Loc: South Carolina
Wouldn't that make the 80 - 125 amp plug on breakers useless?

#72852 - 12/13/06 04:52 AM Re: 200a sub lugs
iwire Offline

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Eddy I have never seen a per stab ratting as low as 70.

I have seen 100 per stab but that does not prevent larger breakers.

A 2 pole 150 amp breaker for a 200 amp panel will use two stabs per phase.
Bob Badger
Construction & Maintenance Electrician