#72843 - 12/11/06 03:03 PM 200a sub lugs
harlie_7 Offline
Junior Member
Registered: 12/11/06
Posts: 1
Loc: DELTA OH.
I have a 200A panal in my house and would like to put a 200A sub in my barn. I know seimans dont make a 200A 2pole breaker. Is there a lug kit i can put in this panal to feed the sub? Any other options?
Top
Work Gear for Electricians and the Trades
#72844 - 12/11/06 03:30 PM Re: 200a sub lugs
Roger Offline
Member
Registered: 05/18/02
Posts: 1716
Loc: N.C.
Harlie, contact a local Electrician, they will be able to help you.

Roger
Top
#72845 - 12/12/06 04:42 PM Re: 200a sub lugs
circuit man Offline
Member
Registered: 11/05/01
Posts: 273
Loc: saluda,s.c.
harlie, why not put a seperate meter on the barn? copper is pretty expensive for a 200 amp feed,unless it's real short. but as roger said please contact an electrician
Top
#72846 - 12/12/06 07:00 PM Re: 200a sub lugs
ShockMe77 Offline
Member
Registered: 06/11/05
Posts: 821
Loc: Rahway, New Jersey
What kinds of loads will there be in the barn?
Top
#72847 - 12/12/06 07:26 PM Re: 200a sub lugs
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
I can't think of a reason that you would want to put in a 200A subpanel fed from a 200A panel.
If your load in the barn is that great, chances are you would need to upgrade the service at the house.
I don't know if it's an alternative, but will the PoCo give you a separate service at the barn?
Top
#72848 - 12/12/06 09:05 PM Re: 200a sub lugs
SolarPowered Offline
Member
Registered: 07/05/04
Posts: 625
Loc: Palo Alto, CA, USA
I'm guessing that Harlie has, or has his eye on, a "200A panel", and figures that he needs to supply it with a 200A supply.

Harlie, that's not necessary. Your supply needs to be sized according to the load calcs in the Code, which will almost certainly be less than 200A. It is very likely you can feed your 200A panel with a 50-100A feeder.

[This message has been edited by SolarPowered (edited 12-13-2006).]
Top
#72849 - 12/12/06 11:32 PM Re: 200a sub lugs
e57 Offline
Member
Registered: 05/27/03
Posts: 2876
Loc: S.F.,CA USA
"seimans dont make a 200A 2pole breaker."

They don't?!? http://www.sea.siemens.com/resident/images/Circuit%20Breaker/Q2200B.jpg
http://www.sea.siemens.com/resident/images/Circuit%20Breaker/MBK200A.jpg

http://www.sea.siemens.com/resident/images/Circuit%20Breaker/QN2200.jpg

http://www.sea.siemens.com/resident/images/Circuit%20Breaker/QN2200R.jpg

Edit due to pic's being so big you could see the finger-prints of the photographer.....



[This message has been edited by e57 (edited 12-13-2006).]
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason
Top
#72850 - 12/13/06 03:47 AM Re: 200a sub lugs
Eddy Current Offline
Member
Registered: 09/26/06
Posts: 111
Loc: Ontario,Canada
All panels have a "per stabb" rating on the inside of the cover. A 200a panel usually has a max of about 70a per stabb. You can't run a 200a circuit from a 200a pqnel. Check the "per stabb" rating on the panel.
Top
#72851 - 12/13/06 04:43 AM Re: 200a sub lugs
watthead Offline
Member
Registered: 10/13/01
Posts: 172
Loc: South Carolina
Eddy
Wouldn't that make the 80 - 125 amp plug on breakers useless?
Top
#72852 - 12/13/06 04:52 AM Re: 200a sub lugs
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
Eddy I have never seen a per stab ratting as low as 70.

I have seen 100 per stab but that does not prevent larger breakers.

A 2 pole 150 amp breaker for a 200 amp panel will use two stabs per phase.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 94 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals