The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/24/16 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
ghost307 7
HotLine1 7
renosteinke 6
Potseal 4
Who's Online
1 registered (gfretwell), 318 Guests and 3 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#72654 - 12/06/06 11:57 AM Extension Cords-Which to Use First?
wendel Offline

Registered: 08/07/04
Posts: 57
I have two extension cords both are 50 feet long. One is 12 gauge and the other is 14 gauge. I want to power an electric saw.

I want the least voltage drop over the combined 100 feet so I keep the current draw by the saw motor as low as possible minimizing heat damage. Which should I plug into the 120 volt receptical first? Why?

Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#72655 - 12/06/06 12:16 PM Re: Extension Cords-Which to Use First?
scameron81 Offline

Registered: 02/24/04
Posts: 80
Loc: Healdsburg, ca, USA
I don't think it matters. The resistance will be the sum of the two extension cords regardless of which one comes first and the distance is still the same. But I could be wrong (it wouldn't be the first time.)

#72656 - 12/06/06 12:53 PM Re: Extension Cords-Which to Use First?
SvenNYC Offline

Registered: 08/19/02
Posts: 1685
Loc: New York City's still, essentially two resistors in series. Don't think it really matters which "gets it" first.

If it makes you feel better, though, I'd go with the #12 first and then hook in the #14.

Of course I betcha the wiring in the wall is #14....

Would there really be THAT much voltage drop over that much wire?

#72657 - 12/06/06 01:15 PM Re: Extension Cords-Which to Use First?
pauluk Offline

Registered: 08/11/01
Posts: 7693
Loc: Norfolk, England
It's all going to be one series circuit whichever way you do it:

#1. Hot -> 50' #12 -> 50' #14 -> Tool -> 50' #14 -> 50' #12 -> Neutral.

#2. Hot -> 50' #14 -> 50' #12 -> Tool -> 50' #12 -> 50' #14 -> Neutral.

Either way you have 100 ft. of #14 plus 100 ft. of #12 conductor in the circuit, so the resistance of the extension cords will be the same.

#72658 - 12/06/06 01:36 PM Re: Extension Cords-Which to Use First?
rabbitgun Offline

Registered: 07/25/06
Posts: 21
Nope it does not matter.
That said, even with a 16A load the drop is only right around 4 volts.

#72659 - 12/07/06 12:15 AM Re: Extension Cords-Which to Use First?
e57 Offline

Registered: 05/27/03
Posts: 2837
Loc: S.F.,CA USA
Have you thought of installing an outlet closer?
Mark Heller
"Well - I oughta....." -Jackie Gleason

#72660 - 12/07/06 06:34 AM Re: Extension Cords-Which to Use First?
Zapped Offline

Registered: 10/01/02
Posts: 481
Loc: Huntington Beach, CA, USA
Two resistors in series: R(total)=R1+R2. No difference with placement. If it's causing you to lose sleep, spend the $20 on another 50' #12 extension.

#72661 - 12/08/06 03:56 PM Re: Extension Cords-Which to Use First?
napervillesoundtech Offline

Registered: 02/28/06
Posts: 144
Loc: Naperville, IL, USA
Think about inrush current, though. Get a 100' 10/3 cord. just a thought.