#72654 - 12/06/06 11:57 AM Extension Cords-Which to Use First?
wendel Offline
Member
Registered: 08/07/04
Posts: 55
I have two extension cords both are 50 feet long. One is 12 gauge and the other is 14 gauge. I want to power an electric saw.

I want the least voltage drop over the combined 100 feet so I keep the current draw by the saw motor as low as possible minimizing heat damage. Which should I plug into the 120 volt receptical first? Why?
Top
Work Gear for Electricians and the Trades
#72655 - 12/06/06 12:16 PM Re: Extension Cords-Which to Use First?
scameron81 Offline
Member
Registered: 02/24/04
Posts: 75
Loc: Healdsburg, ca, USA
I don't think it matters. The resistance will be the sum of the two extension cords regardless of which one comes first and the distance is still the same. But I could be wrong (it wouldn't be the first time.)
Top
#72656 - 12/06/06 12:53 PM Re: Extension Cords-Which to Use First?
SvenNYC Offline
Member
Registered: 08/19/02
Posts: 1691
Loc: New York City
Yeah....it's still, essentially two resistors in series. Don't think it really matters which "gets it" first.

If it makes you feel better, though, I'd go with the #12 first and then hook in the #14.

Of course I betcha the wiring in the wall is #14....

Would there really be THAT much voltage drop over that much wire?
Top
#72657 - 12/06/06 01:15 PM Re: Extension Cords-Which to Use First?
pauluk Offline
Member
Registered: 08/11/01
Posts: 7520
Loc: Norfolk, England
It's all going to be one series circuit whichever way you do it:

#1. Hot -> 50' #12 -> 50' #14 -> Tool -> 50' #14 -> 50' #12 -> Neutral.

#2. Hot -> 50' #14 -> 50' #12 -> Tool -> 50' #12 -> 50' #14 -> Neutral.

Either way you have 100 ft. of #14 plus 100 ft. of #12 conductor in the circuit, so the resistance of the extension cords will be the same.
Top
#72658 - 12/06/06 01:36 PM Re: Extension Cords-Which to Use First?
rabbitgun Offline
Member
Registered: 07/25/06
Posts: 23
Nope it does not matter.
That said, even with a 16A load the drop is only right around 4 volts.
Top
#72659 - 12/07/06 12:15 AM Re: Extension Cords-Which to Use First?
e57 Offline
Member
Registered: 05/27/03
Posts: 2876
Loc: S.F.,CA USA
Have you thought of installing an outlet closer?
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason
Top
#72660 - 12/07/06 06:34 AM Re: Extension Cords-Which to Use First?
Zapped Offline
Member
Registered: 10/01/02
Posts: 482
Loc: Huntington Beach, CA, USA
Two resistors in series: R(total)=R1+R2. No difference with placement. If it's causing you to lose sleep, spend the $20 on another 50' #12 extension.
Top
#72661 - 12/08/06 03:56 PM Re: Extension Cords-Which to Use First?
napervillesoundtech Offline
Member
Registered: 02/28/06
Posts: 144
Loc: Naperville, IL, USA
Think about inrush current, though. Get a 100' 10/3 cord. just a thought.
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 54 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals