#72121 - 11/19/06 08:43 AM Stripped neutrals
village-electric Offline
Junior Member
Registered: 10/16/06
Posts: 4
Loc: Sedona, AZ
Doing remodel work at a residence.

This is one one houses that have additions slapped on and on....

Anyway, original service was an 200A all-in-one behind garage. An addition was built on back of garage so the meter/disconnect was relocated to back deck.

Now the original panel is a sub (with 2 subs of of it), I know that the neutrals / grounds need to be seperated but find that all of the neutrals have been stripped back to the knockout. So this panel is full of bare conductors. Should be loads of fun trying to seperate / tail these as all of the brach circuits come in through a 2-1/2" ko in back of panel.

Anyone seen this before?
Top
Work Gear for Electricians and the Trades
#72122 - 11/19/06 09:15 AM Re: Stripped neutrals
Theelectrikid Offline
Member
Registered: 04/30/04
Posts: 854
Loc: Levittown, PA
I'm not an electrician,

I've never seen this,

But I probably wouldn't want to do it. If somebody's working (testing) in that panel live, touching the bare neutral could make you the new return path, equating a touch to the LINE lugs on the main breaker.

Ian A.
_________________________
Is there anyone on board who knows how to fly a plane?
Top
#72123 - 11/19/06 09:27 AM Re: Stripped neutrals
Sparks30 Offline
Member
Registered: 03/23/02
Posts: 125
Loc: Connecticut.usa
First are you sure that they didn,t use se to feed the subs. If it is a stripped back nuet then shut off the sub and tape the wire with good slipe tape . This will make itsafe to work on.
Top
#72124 - 11/19/06 11:29 AM Re: Stripped neutrals
village-electric Offline
Junior Member
Registered: 10/16/06
Posts: 4
Loc: Sedona, AZ
thanks for the replies.

Yes, 4 wire feeder was used. There are 2 se in the panel feeding the a/c and the range. The romex branch circuits coming in the back of the panel all but 2 have the neutrals stripped. Believe me, I had to look twice.
Top
#72125 - 11/19/06 01:52 PM Re: Stripped neutrals
Theelectrikid Offline
Member
Registered: 04/30/04
Posts: 854
Loc: Levittown, PA
Oh, forgot this:

Welcome to ECN!

Ian A.
_________________________
Is there anyone on board who knows how to fly a plane?
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Looking for older post
by sparkyinak
Today at 12:27 AM
License exam
by TRUE POWER
Yesterday at 11:33 PM
Members: Non-Members: Did you know?
by Admin
Yesterday at 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM

Who's Online
2 registered (Admin, HotLine1), 90 Guests and 13 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Tom
Tom
Member Since: 01/01/01
Posts: 1069

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals