#7190 - 01/25/02 06:02 AM burned out bulbs
buddy Offline
Member
Registered: 09/11/01
Posts: 8
This is probably a simple question for this group. A co-worker recently had a residence rewired and has experienced the light bulbs in one hallway burning out every couple of weeks. Any thoughts on what is causing this?
Top
Work Gear for Electricians and the Trades
#7191 - 01/25/02 07:59 AM Re: burned out bulbs
George Corron Offline
Member
Registered: 05/16/01
Posts: 717
Loc: Lorton, Va USA
Loose neutral (in home run, splice, etc.) poorly made edison base sockets for the bulbs, poorly made, maybe imported light bulbs.
Top
#7192 - 01/25/02 10:56 AM Re: burned out bulbs
Bill Addiss Offline
Member
Registered: 10/07/00
Posts: 3875
Loc: NY, USA
Bulbs could be loose or subject to vibration somehow from the floor above, slamming doors, etc. Try a rough service bulb in the fixture.

Bill
Top
#7193 - 01/25/02 07:57 PM Re: burned out bulbs
NoShorts4Me Offline
Member
Registered: 01/14/02
Posts: 36
Loc: southern california
As the others said. Most likely a loose neutral somewhere, obviously try looking at the fixture first. Last resort, try a 130v incandescent lamp. Covers many a problem.
Cheers
NS4M
Top
#7194 - 01/26/02 07:13 AM Re: burned out bulbs
Steve Miller Offline
Member
Registered: 08/30/01
Posts: 325
Loc: Loudoun Cty, VA
NS4M has the right idea. There is a formula for incandescent bulbs in our apprenticeship books that says:
(Actual Life/Rated Life) = (Rated Volts/Actual Volts)^13.

Take a 130 volt, 1000hr rated bulb and feed it 123 volts and you get:
AL/1000=(130/123)^13 or 2053 hours actual life.

In contrast, take a 120 volt 1000hr bulb and feed it 123 volts and you get:
AL/1000=(120/123)^13 or 725 hours actual life.

Those 130v bulbs are life savers in hard to reach fixtures.
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 61 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals