The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 235 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#71860 - 11/08/06 10:54 AM Ansul System
bot540 Offline
Member

Registered: 09/14/04
Posts: 177
Loc: Vernon Hills, IL
I am doing a commercial kitchen with an ansul system for the first time and had a few questions. The inspector want all power to the hood and exhaust fans to shut down. How is this usually acomplished, with contactors and a low voltage signal? Does anyone know where I can find wiring diagrams?
Thanks.
_________________________
Jesus may have been a capenter,but God was an electrician.Genesis1:3

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#71861 - 11/08/06 11:20 AM Re: Ansul System
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
The ansul panel will have electrical contacts in it, usually a few SPDT micro switches.

The most common way I handle it is by the use of shunt trip breakers controlled at 120 volts through the ansul contacts.

Be sure to find out exactly what needs to be shut down.

In my area the power to the appliances under the hood and the make up air supply shut down but exhaust fans and lights stay on.

In other areas they want all power off, before you waste time and money find out for sure what your AHJ wants.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#71862 - 11/08/06 04:56 PM Re: Ansul System
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
I agree with Bob... work closely with your fire guy on this one.

The trip mechanism will usually have two sets of contacts. One set is used in the "normally open" position by the alarm guy; the other is for you.

I use the "normally closed" contacts to interrupt power to my contactor coils. System trips, coils stop working, contactors open, stuff shuts down.

I have had the issue of the exhaust fans go both ways. The make-up air, any power under the hood, hood lights, and the gas valve (if electric- most are mechanical) all get shut off.

Usually, I will use an 8x8 gutter to mount my contactors in. I do this, as usually the power to the various items comes from different panels.

The coils really ought to be on their own dedicated circuit. This is both because it makes it easy to test the system, and you really don't want any nuisance tripping. Lose power, everything under the hood gets shut down.

As for the circuits being interrupted, I cut into them wherever it's most convenient. This could very well be at the panel, and nowhere near the appliance at all.

Top
#71863 - 11/08/06 05:40 PM Re: Ansul System
HCE727 Offline
Member

Registered: 11/11/05
Posts: 190
Loc: Delaware County, PA, USA
BOT, I have something from ANSUL, if you have a fax, I will fax it to you. E-mail me.
_________________________
Hank

Top



ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals