#7181 - 01/25/02 05:58 AM 4w ser or 3w seu
Cindy Offline
Member
Registered: 06/23/01
Posts: 196
Loc: PDX, OR, US
why can't you use 3w seu with a separate 4awg egc from a service to a subpanel [with an isolated gc]? the egc shouldn't be current carrying so there shouldn't be a problem with impedance or inductive heating... that's why we keep them in the same 4w ser cable, right?
Top
Work Gear for Electricians and the Trades
#7182 - 01/25/02 08:47 AM Re: 4w ser or 3w seu
Redsy Offline
Member
Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
It isn't carrying current under normal conditions. However, in the event of a fault, the fault current may be limited by the reactance of the single conductor, if it is not in close proximity to the conductor feeding the fault. The OCPD might not open in such a case.
Top
#7183 - 01/25/02 04:55 PM Re: 4w ser or 3w seu
Cindy Offline
Member
Registered: 06/23/01
Posts: 196
Loc: PDX, OR, US
thank you redsy
Top
#7184 - 01/25/02 06:34 PM Re: 4w ser or 3w seu
The Watt Doctor Offline
Member
Registered: 12/23/01
Posts: 443
Loc: Mont Belvieu, TX
Miss Cindy,
If I may ask, where is the subpanel located?
_________________________
The Watt Doctor
Altura Cogen
Channelview, TX
Top
#7185 - 01/25/02 08:24 PM Re: 4w ser or 3w seu
Cindy Offline
Member
Registered: 06/23/01
Posts: 196
Loc: PDX, OR, US
this was in a new house i walked through a few days ago, the meter and 200amp disconnect combo were surface mounted on the side of the garage, and the seu and 4awg cu were run across the garage in the joist bay above, and came down the wall to the 200amp loadcenter, with the isolated gc. it wasn't my job, and i didn't want to stir anything up, so didn't say anything to the contractor.... but i didn't think it was right. if i thought it was real dangerous then i would have said something, thats why i asked here, cause i wouldn't have been able to explain to him why it was a bad idea
Top
#7186 - 01/26/02 06:54 AM Re: 4w ser or 3w seu
Steve Miller Offline
Member
Registered: 08/30/01
Posts: 322
Loc: Loudoun Cty, VA
This is 300-3(b)(1999) Notice it says 'and all EGCs'. I haven't seen your installation but it sounds like this would cover your situation.


(b) Conductors of the Same Circuit. All conductors of the same circuit and, where used, the grounded conductor and all equipment grounding conductors shall be contained within the same raceway, auxiliary gutter, cable tray, trench, cable, or cord, unless otherwise permitted in accordance with (1) through (4).
Top
#7187 - 01/26/02 05:28 PM Re: 4w ser or 3w seu
Elzappr Offline
Member
Registered: 12/20/01
Posts: 273
Loc: Oregon
Aside from the code issue, it seems like a commonsensical thing to do,'til you get to the point of putting the wiring into the boxes. Doesn't seem likely that they could ever adequately close off the box opening, or adequately clamp the cable, with that extra conductor added to the cable. Of course, I'm sure UL hasn't tested such a set-up, so there's no way to be assured that the connection would work.
Top
#7188 - 01/26/02 06:25 PM Re: 4w ser or 3w seu
Bill Addiss Offline
Member
Registered: 10/07/00
Posts: 4196
Loc: NY, USA
Cindy,

Aside from other considerations, with SEU cable they don't have an insulated grounded (Neutral) conductor.

Bill
Top
#7189 - 01/27/02 08:12 PM Re: 4w ser or 3w seu
The Watt Doctor Offline
Member
Registered: 12/23/01
Posts: 443
Loc: Mont Belvieu, TX
Cindy,
Well, I will agree with Steve on this one. The reason that I asked the question above was to get a clear picture of the situation.
_________________________
The Watt Doctor
Altura Cogen
Channelview, TX
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Looking for older post
by sparkyinak
Today at 12:27 AM
License exam
by TRUE POWER
Yesterday at 11:33 PM
Members: Non-Members: Did you know?
by Admin
Yesterday at 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM
International Wire Colour Codes
by Texas_Ranger
01/21/17 03:29 PM

Who's Online
1 registered (Ruben Rocha), 155 Guests and 12 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Tom
Tom
Member Since: 01/01/01
Posts: 1069

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals