ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#71569 - 11/01/06 04:00 PM electric range question
trekkie76 Offline
Member
Registered: 06/19/04
Posts: 220
Loc: baileyville, maine, usa
Was on a service call today and I need a little input from the smart people here.
Situation:Electric range was giving lady a shock when she touched the pot on the stovetop. Measured 40 VAC from the burner surface to the frame. This is a 3 wire setup, with the ground and neutral bonded at the stove. The feed is from 120Y/208.

Could there be any current coming back on the neutral from the elements? I checked the elements, nothing rang out to ground. And it only did it on the 2 larger burners.
It also had a digital clock/timer in it. Could it somehow have cuased current to flow on the nuetral and thus through the frame?

Thanks for any help gentlemen, Gary
Top
Work Gear for Electricians and the Trades
#71570 - 11/01/06 04:23 PM Re: electric range question
BigB Offline
Member
Registered: 03/31/04
Posts: 719
Loc: Tucson, AZ USA
Trek...what shape were the burners in? I have seen this happen when the burners are badly corroded or have holes in the outer covering.
Top
#71571 - 11/01/06 04:43 PM Re: electric range question
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
I agree with BigB.

It sounds like bad elements.

You could try testing from the range frame to a known good ground....maybe the ground in an extension cord that was plugged into a known grounded outlet.

This would make sure you don't have a bad neutral/ground to the stove
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#71572 - 11/01/06 05:20 PM Re: electric range question
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9038
Loc: Estero,Fl,usa
The root cause is probably a bad element but that should be caught by the grounding. I had a problem in my house with this that traced back to a bad ground clamp on the grounding electrode. The whole house was "hot to ground" and the place it showed up was standing on the terazzo floor barefooted, touching the stove.
A real morning "waker upper".
The fact that the burner is hot to the stove frame seems to indicate this is a more localized failure. The real answer might be as simple as throwing away the bad element. Those burner pans sitting on the enamaled stove surface are not really a grounding path.

[This message has been edited by gfretwell (edited 11-01-2006).]
_________________________
Greg Fretwell
Top
#71573 - 11/01/06 07:22 PM Re: electric range question
Dave T Offline
Member
Registered: 01/22/05
Posts: 155
Loc: Waukesha, WI, USA
If it were a 3w set up where the neutral and EGC share the same conductor I would confirm the integrity of that wire back to the panel. If any the connections this conductor are compromised and 120v loads that are L-N can provided the opportunity for current to pass through a person who is touching the appliance and a grounded item at the same time instead to that current returning by way of that neutral/EGC conductor. If this is the failure then it substantiates why a separate neutral and EGC are superior.
Top
#71574 - 11/02/06 12:42 AM Re: electric range question
Trumpy Offline


Member
Registered: 07/05/02
Posts: 8211
Loc: SI,New Zealand
My 2c worth,
I am assuming that you are talking about electric elements not gas burners?.
To my way of thinking, the outside of the elements should be at ground potential, hence there should be no shock hazard.
What is going on if there is 40V with respect to ground?.
What did you test this with?.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin
Top
#71575 - 11/02/06 02:27 AM Re: electric range question
RODALCO Offline
Member
Registered: 12/08/05
Posts: 854
Loc: Titirangi, Akld, New Zealand
Are these plug in elements ?
If so the scraping earth may be corroded and not making a low resistance contact to keep the outer element casing at earth potential.
If an element is on the way out, the internal resistance wire may be touching somewhere to the outer casing.
Sometimes that is very visible as a hotspot which is a lot brighter light yellow orange than the rest of the elements while on full power.
When the earth is high resistance there may be a certain amount of leakage which may cause part of the power to leak through the casing to earth and a higher current will be drawn from the supply untill the element burns out, and will cause a rise in potential of the actual element casing.

edited for typo's RF.

[This message has been edited by RODALCO (edited 11-02-2006).]
_________________________
The product of rotation, excitation and flux produces electricty.
Top
#71576 - 11/02/06 09:46 AM Re: electric range question
EV607797 Offline
Member
Registered: 10/25/06
Posts: 744
Loc: Fredericksburg, VA, USA
Burners in electric ranges and ovens run at 208 or 240 volts. The only need for a neutral at all is for the 120 volt accessories, such as clocks, lights and timers. My guess would be that the neutral is open or has a fault so the neutral isn't able to provide a return path from one or all of the 120 volt accessories. Does the clock and light work properly?

I am concerned that you mentioned 120/208 since this would indicate a three-phase service. Is this in a multi-tenant building? If so, the panel in this unit would effectively be a sub panel. In this case, there should be a fourth wire for the ground connection to the range.
_________________________
---Ed---

"But the guy at Home Depot said it would work."
Top
#71577 - 11/02/06 11:52 AM Re: electric range question
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
IF the problem was in the branch circuits neutral / ground you would not see 40 volts between the frame and the burner.

IF the problem was in the branch circuits neutral / ground you might find 40 volts between the frame and a 'good' ground or 40 volts between the burner and a good ground.

However the fact that there is 40 volts between a burner and the ranges frame suggest the problem is internal to the range and likely the burner itself.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#71578 - 11/02/06 12:27 PM Re: electric range question
EV607797 Offline
Member
Registered: 10/25/06
Posts: 744
Loc: Fredericksburg, VA, USA
Uh, I guess I should have paid closer attention to the original post "from the BURNER to the top". I was in the mindset the the top was energized and the measurement was being taken from it to perhaps the sink plumbing. That makes a big difference.

No doubt, the burner(s) has failed. Most appliances only switch one leg of the 208/240 feeding them, so a fault would certainly be capable of energizing the coil itself even if turned off.

Another plug for smooth top ranges, I suppose.
_________________________
---Ed---

"But the guy at Home Depot said it would work."
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 94 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals